Generator Not Maintaining Correct Speed for Load

10/08/2011 6:06 PM

I have a cat 3406B with a 300kw MagnaMax generator.

It was on line for a little over 24hrs, when i heard a change in tone, like a heavy load was just put on it, and not recovering speed wise. when i got to the engine room, checked over the engine, noticed that all gauges were normal (fuel pressure). At the switch board, i saw the Hz were down to 55, but Kw, and Amp, meters were about normal at the time (probably 50% load on it) but the lights were dimming from the lower speed. I put my other generator on line, and took that one off.

I checked wire connections on the gen voltage regulator, and connections to the Woodward 2301A. all looked fine, and had proper voltage to 2301A.

I started the engine back up, brought it up to rated speed, and noticed "NON" of the meters on the switchboard panel were working at all. i turned on the syncroscope to take a look to see if the meters were just messed up, but it wouldnt even appear to be able to sync.

does anyone have any ideas what this problem could be? Voltage Reg? 2301A?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Generator not maintaining correct speed for load

10/08/2011 7:55 PM

Since the electric loads are the same for both generators and the ailing generator displayed normal electric load condition but a below normal frequency display that agreed with the sound of a slow engine, I suspect that you have a problem with the engine and not the generator.

Did you contact the manufacturer (Caterpillar?) or any mechanic?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Member
Engineering Fields - Marine Engineering - New Member

Join Date: Oct 2011
Posts: 7
#2
In reply to #1

Re: Generator not maintaining correct speed for load

10/08/2011 8:19 PM

Yes. Am waiting to hear back from them. While looking things over again. noticed that my actuator may have been limiting out. i readjusted the linkage between the fuel rack and actuator. Not sure if this was the problem, but everthing seems to work again.

Before, i wasnt seeing any voltage on the switchboard. normally at idle, i see around 290V. but was getting nothing before. now everything seems to work. I still dont know if i trust it enough to but back on line by itself.

Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#3
In reply to #2

Re: Generator not maintaining correct speed for load

10/08/2011 8:42 PM

It sounds like you've something else going on, unless someone snuck in and adjusted the actuator linkage while you had your back turned. Are you sure that the governor is handling the load on the engine? For you to adjust the actuator linkage and it seems to fix it, leads me to think that the governor isn't doing it's thing by increasing the throttle.

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Member
Engineering Fields - Marine Engineering - New Member

Join Date: Oct 2011
Posts: 7
#4
In reply to #3

Re: Generator not maintaining correct speed for load

10/08/2011 8:53 PM

The actuator had been changed out about a week ago. So i was thinking that it wasn't positioned right. hadn't run that engine under much load since then

Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#5
In reply to #4

Re: Generator not maintaining correct speed for load

10/08/2011 8:59 PM

Why was the actuator changed out? Do you have any means of load testing the gen-set?

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6
In reply to #2

Re: Generator not maintaining correct speed for load

10/08/2011 9:01 PM

Allow me to suggest a stab in the dark. The adjustment on the fuel rack actuator may have just vibrated loose over time. Until the vibrations moved the adjustment far enough that the mechanical control could not compensate for the movement the effect of this adjustment loss was not noticed.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7

Re: Generator not maintaining correct speed for load

10/08/2011 9:50 PM

If the gensets can now be paralleled successfully, you could back off on the other generator and see how well the repaired one picks up and holds the loads. If it maintains speed, voltage, and kw, it looks good to go.

(Earlier I wondered about fouled injectors, which could happen while still having normal fuel pump pressure. The further info made that seem unlikely.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster #1
#8

Re: Generator not Maintaining Correct Speed for Load

10/09/2011 7:41 AM

i think it's a generator problem. if the generator is mal-funtioning [low hz] for example, the engine would speed up as it tries to maintain the required output.

Register to Reply Off Topic (Score 4)
Member
Engineering Fields - Marine Engineering - New Member

Join Date: Oct 2011
Posts: 7
#9

Re: Generator not Maintaining Correct Speed for Load

10/09/2011 4:58 PM

After re positioning the actuator linkage, it seems to be fine now. i put it online by itself, and maintained like normal. i still feel there was something else going on for none of the meters to be showing anything.

the actuator was originally replaced trying to troubleshoot a previous problem, but was found not to be the problem. it was a 12v ground to the load sharing switch, causing that gen to want to always share load.

the generator itself still makes me suspicious. it was installed early July and was kind of rushed in. i was not here for that, but still think its something to do with it, i have never had these kind of problems with my generators until this one was put onboard

Thank you for all the comments and suggestions though......

Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#10

Re: Generator Not Maintaining Correct Speed for Load

10/09/2011 11:04 PM

Well, sooner or later, preferably with an engine tech present you will have turn the set on. Since it is a frequency problem, load is not needed at first.

There is a recurring remark that bothers me. You say, that then and then the meters show nothing (abnormal, or what??) outside the low freq??

Register to Reply
Member
Engineering Fields - Marine Engineering - New Member

Join Date: Oct 2011
Posts: 7
#15
In reply to #10

Re: Generator Not Maintaining Correct Speed for Load

10/10/2011 5:04 PM

for the voltage meter to show nothing at idle, is abnormal. normally around 290V. when engine is at rated speed, normal readings are 480V, 60Hz

Register to Reply
Participant

Join Date: Jun 2011
Posts: 2
#11

Re: Generator Not Maintaining Correct Speed for Load

10/10/2011 1:03 AM

Please let me know the rated speed and voltage.

Register to Reply
Member
Engineering Fields - Marine Engineering - New Member

Join Date: Oct 2011
Posts: 7
#13
In reply to #11

Re: Generator Not Maintaining Correct Speed for Load

10/10/2011 4:57 PM

rated speed is 1800rpm, and voltage is 480. control voltage to the acutator is 24vdc

Register to Reply
Associate

Join Date: Sep 2011
Location: Ontario
Posts: 52
Good Answers: 2
#12

Re: Generator Not Maintaining Correct Speed for Load

10/10/2011 4:42 PM

Your sync instrumentation does not usually show anything before you are at about 58Hz so that may account for the no show.

The cause for the sudden change in speed would make me suspicious of the original fault not being fixed, but due to an intermittent short somewhere. The generator wanting to share load lowers speed due to droop and having no other machine to share with it just drops the frequency..... but dropping to 55Hz seems to be way too much, larger machines would be destroyed by that. Can your frequency meter even read down to 55Hz?

__________________
Fools rush in where wise men fear to go...
Register to Reply Score 1 for Good Answer
Member
Engineering Fields - Marine Engineering - New Member

Join Date: Oct 2011
Posts: 7
#14
In reply to #12

Re: Generator Not Maintaining Correct Speed for Load

10/10/2011 5:01 PM

55Hz is the bottom of the range on my meter. when i was observing the problem, i could notice the meter kind of surging between 55Hz and up to about 58Hz.

Register to Reply
Associate

Join Date: Sep 2011
Location: Ontario
Posts: 52
Good Answers: 2
#16

Re: Generator Not Maintaining Correct Speed for Load

10/10/2011 6:09 PM

If the problem seems to have gone away for the moment you could try and run the machine in parallel with another one, sharing the load 50/50. Then start a large pump and see how they share the increase, this should give you some idea of how well the governor is responding. I am thinking the governor bushing may be sticking sometimes and not responding to load changes when stuck.

You could also try to disconnect the governor and the linkage and move the linkage by hand (with the machine stopped, of course) to ensure there is no sticking in the movements

__________________
Fools rush in where wise men fear to go...
Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#17
In reply to #16

Re: Generator Not Maintaining Correct Speed for Load

10/10/2011 6:58 PM

This was my same thoughts in my post #3, sounded like the governor wasn't responding to the load increase.

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Register to Reply 17 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!