Mounting Busbar For Ground, Outside Panel

10/17/2011 11:41 AM

I know this sounds a little hokey, but I can't think of a reason why not.

I need to run a dedicated circuit for my refrigerator today. I've got several slots open for fuses, but the busbar is full.

Can I mount a separate busbar outside the panel, tie it to the one inside, and only use it for ground wires? The neutrals would stay inside the panel.

This would be far easier than taking everything apart in the panel and installing a larger bar.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Pathfinder Tags: Grounding outside main panel
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#1

Re: Mounting Busbar For Ground, Outside Panel

10/17/2011 12:27 PM

kramarat,

Can you fit one of these in your existing panel?

This would be the safest and legal way to do this.

You don't need one this big. I have seen these at about 2 inches long.

Just run a #10 jumper from the existing bus.

I know there is a reference prohibiting mounting this exposed in the 2011 NEC but can't remember where exactly. When I get back in I will look it up.

Regards KJK

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply Good Answer (Score 2)
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#12
In reply to #1

Re: Mounting Busbar For Ground, Outside Panel

10/17/2011 4:37 PM

Yes I can. How did I not notice the picture this morning? Duh!!!!

Yes. That would be a piece of cake. Looks like it's within code too.....I think.

Here I am, 10 posts later, and looking at this exact option.

Are you sure it's good to go with the codes? If so, that's my answer.

Thanks Kevin

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Mounting Busbar For Ground, Outside Panel

10/17/2011 12:35 PM

Do you know any electricians around there you could ask?

Or, maybe go to the local electrical supply house and ask them what you need to buy from them to do this.

Just insulate it with some of the compresssed plastic bags you store in your nooks and carnnies.

Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#7
In reply to #2

Re: Mounting Busbar For Ground, Outside Panel

10/17/2011 2:39 PM

I asked a couple a little while ago in Lowes. Completely clueless.

Most "real" electricians know enough to run wire and do new construction. When it comes to something outside of that, they don't tend to have any idea.

Not that I blame them. I'm sure they have the stuff that they do every day, memorized.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#8
In reply to #7

Re: Mounting Busbar For Ground, Outside Panel

10/17/2011 3:19 PM

I had in mind a real wholesale electrical supply house that real electrical contractors use.

Neither Lowe's nor Home Depot have competent help. They have clerks.

Don't fry yourself.

Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#9
In reply to #8

Re: Mounting Busbar For Ground, Outside Panel

10/17/2011 3:39 PM

No. I don't ask clerks anything. These were electricians that were in there buying parts.

I'm not going to fry myself. Everything will be shut off. It's easy enough to do. More of a code question. Since all ground goes to an exposed rod in the yard, I wouldn't think it would be a big deal. Of course I can't look up anything in the NEC without buying the book.

I've got spaces for 30 different fuses in the panel, and a total of about 27 bar holes for both neutral and ground. I think it's okay to double up grounds in the panel at the bar, but not neutrals. If I take it apart, I'm putting in the biggest bars I can safely fit.

It's a mess anyway. I probably just need to bite the bullet and do it right.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#3

Re: Mounting Busbar For Ground, Outside Panel

10/17/2011 1:23 PM

Not legally...but you can do it

The point the NEC would make about that is ground fault currents would be in an exposed area...not cool. You could also have low level fault currents outside of the box, but so low as to not cause the breaker to trip. That's the kind of stuff the NEC tries to prevent.

Putting in an additional grounding bar as see above is legal and much safer.

Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#4

Re: Mounting Busbar For Ground, Outside Panel

10/17/2011 1:42 PM

Unfortunately there's no room to add a bar. The idiots that built the house didn't install a bar that was big enough to accommodate all of the neutrals and grounds.

I figured this would probably be against code. I was thinking maybe if I mounted another external bar in a junction box and strictly used it for ground wires, I might be okay. But I don't want to do anything that's going to pop up on an inspection report if I ever decide to sell the place.

The panel needs to be tidied up anyway. This would just make it a little easier.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#5
In reply to #4

Re: Mounting Busbar For Ground, Outside Panel

10/17/2011 2:01 PM

You can run the ground into another panel which is suitably rated, but the problem is the proximity to the circuit feeding that which is grounded in the panel.

i.e., the ground must return to the source.

Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#6
In reply to #5

Re: Mounting Busbar For Ground, Outside Panel

10/17/2011 2:13 PM

Yeah. I can make room in the panel for a larger bar or separate ground bar, but everything has to come apart to do it.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
2
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#14
In reply to #6

Re: Mounting Busbar For Ground, Outside Panel

10/17/2011 4:46 PM

Sometimes the hardest way is the right way, unfortunately.

However, here is an interesting portion of the NEC:

250.114 Equipment Connected by Cord and Plug.

Under any of the conditions described in 250.114(1) through (4), exposed, normally non-current-carrying metal parts of cord-and-plug-connected equipment shall be connected to the equipment grounding conductor.

Exception: Listed tools, listed appliances, and listed equipment covered in 250.114(2) through (4) shall not be required to be connected to an equipment grounding conductor where protected by a system of double insulation or its equivalent. Double insulated equipment shall be distinctively marked.

(3) In residential occupancies:

a. Refrigerators, freezers, and air conditioners

So, there is a chance that a grounding connector is not required at all. This is, of course, unless it violates the warranty of the refrigerator, your insurance policy, common sense, etc.

Otherwise:

408.40 Grounding of Panelboards.

Panelboard cabinets and panelboard frames, if of metal, shall be in physical contact with each other and shall be connected to an equipment grounding conductor. Where the panelboard is used with nonmetallic raceway or cable or where separate equipment grounding conductors are provided, a terminal bar for the equipment grounding conductors shall be secured inside the cabinet. The terminal bar shall be bonded to the cabinet and panelboard frame, if of metal; otherwise it shall be connected to the equipment grounding conductor that is run with the conductors feeding the panelboard.

Register to Reply Good Answer (Score 2)
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#17
In reply to #14

Re: Mounting Busbar For Ground, Outside Panel

10/17/2011 5:14 PM

Thanks a lot pete. That clinches it. KJK was right on. It's nice to see the actual code though.

I have to say, since I'm not a total expert, anything in my house that has a factory ground on the plug, will be grounded at the panel. Better safe than sorry. I don't want to void any warranties either.

I'm already into the beer today, so I guess it'll be tommorrow for this project.

I'm proud to say, that sometimes usually, CR4 just beats the hell out of a google search.

Depending on the nature of the question.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#10

Re: Mounting Busbar For Ground, Outside Panel

10/17/2011 3:48 PM

Last time I did electrical work It's been a few years so the NEC may have changed. You were aloud to run one ground and one neutral per two circuits the feeds off two breakers. Was common practice to run 12/3 romex to a distance and split it into two 120 volt circuits. You may be able to double up some of the ground wires in the panel to find space. If it's changed some one speak up.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#11
In reply to #10

Re: Mounting Busbar For Ground, Outside Panel

10/17/2011 4:15 PM

I think it's still okay to double up grounds, but not neutrals.

I found this on another site. The second answer indicates that it would be alright to mount another ground bar to the inside of the panel box itself. I'm not the OP on the other site. This would work for me also. Again, it's about the codes. I'd rather spend the extra time now, than have to redo it in 20 years, or whenever I sell.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#13
In reply to #11

Re: Mounting Busbar For Ground, Outside Panel

10/17/2011 4:41 PM

kramarat,

Like I said in #1, buy a ground bus extension for about $6 to $8 bucks. They have different sizes.

Find an area in the existing panel, screw it in, run a #10 jumper over. Some of these kits even come with a solid bonding link (about the size of a #10).

Edit: I just walked back into my warehouse and found a (new in the bag with mounting screws) SQ-D PK18GTA Equipment Grounding Bar Kit.

PM me with your address, we will figure out a way to get it out to you. and I will call Lyndoor Express Delivery and get it to you "next day".

I may not respond till tomorrow morning, getting ready to head out for the day.

Regards - KJK

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#15
In reply to #13

Re: Mounting Busbar For Ground, Outside Panel

10/17/2011 4:55 PM

Don't worry about it man. It'll cost more to ship than I can buy one for.

I looked at post #1 this morning, and somehow it didn't register that the bar was attached to the panel box itself. I was thinking it had to be attached to the main ground/neutral, where there's not much space.

I'm still going to clean up the nest in the panel. I'll post a before and after pic tomorrow.

I appreciate the offer to send the one you have, but you know damned well, as soon as you do that, you'll need it.

I was looking at them today at Lowes..................about $6 for what I need.

Thanks again.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#16
In reply to #13

Re: Mounting Busbar For Ground, Outside Panel

10/17/2011 5:07 PM

LynDoor™Express Delivery. When you ABSOLUTELY have to have it overnight.

Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#18
In reply to #16

Re: Mounting Busbar For Ground, Outside Panel

10/17/2011 10:26 PM

I like it!!

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#24
In reply to #10

Re: Mounting Busbar For Ground, Outside Panel

10/18/2011 3:11 PM

In newer codes, if you share a neutral, you must use handle ties or common trip breakers. -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#19

Re: Mounting Busbar For Ground, Outside Panel

10/18/2011 2:27 PM

add a sub panel, which can be handy

Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#22
In reply to #19

Re: Mounting Busbar For Ground, Outside Panel

10/18/2011 2:40 PM

I'm going to put one out in my shop, (100 amp), but I have to finish the inside of the house first.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#20

Re: Mounting Busbar For Ground, Outside Panel

10/18/2011 2:27 PM

All done guys. Took about 4 hours. I overkilled the ground bar, but no big deal. It's on the upper left. Also put in a larger neutral bar, and got everything labeled. Plenty of room for future circuits.

I didn't take a before picture, but it was a birds nest. I eliminated about 20' of wire that was just jammed in there. I couldn't really see the back of the panel box when I started.

Thanks for everyone's input.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#21
In reply to #20

Re: Mounting Busbar For Ground, Outside Panel

10/18/2011 2:40 PM

Your Hired!! Looks Pretty and Nice, Mark. I've worked panels that were what your's was like, they can be a real pain in the A$$! Good Job

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#23
In reply to #20

Re: Mounting Busbar For Ground, Outside Panel

10/18/2011 2:42 PM

looks good

it's always a good idea to make it look like you know what you are doing

Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#25
In reply to #23

Re: Mounting Busbar For Ground, Outside Panel

10/18/2011 3:47 PM

Yeah, now I know why I was scared to work in there...............it was a mess.

Makes my whole brain feel better.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#26
In reply to #20

Re: Mounting Busbar For Ground, Outside Panel

10/18/2011 4:01 PM

You do good work!

Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#27
In reply to #26

Re: Mounting Busbar For Ground, Outside Panel

10/18/2011 4:32 PM

Thanks. I had seen a picture on line of a fuse box. Every wire was cut to the perfect length for each breaker, and bent at a perfect 90° angle where it went into the breaker. It was a piece of art. I wanted to get somewhere close to that look.

Originally, every wire on mine was too long, grounds included. Instead of cutting them, they just wadded the excess wire into balls and jammed it in where it would fit.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#30
In reply to #27

Re: Mounting Busbar For Ground, Outside Panel

10/18/2011 8:53 PM

if you ever have to work with signal [audio] wiring, have them cross the power at 90° for less interference

Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#31
In reply to #30

Re: Mounting Busbar For Ground, Outside Panel

10/19/2011 12:40 AM

My ex racist, police officer friend/neighbor that I have been hanging out with for the past 8 years, was found dead in his house by the cleaning girl this morning.

He came down to the house and had a drink almost every afternoon, on the front porch.

I'm not freaking out, but I'm a little out of sorts at the moment.

I'm glad I have CR4. Not looking for sympathy...................just need to work it through.

I didn't hear the news until this afternoon. Needless to say, the joy that I got from my panel has been tempered by reality.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#32
In reply to #31

Re: Mounting Busbar For Ground, Outside Panel

10/19/2011 9:10 AM

Sorry to hear that. Natural causes?

Register to Reply Off Topic (Score 5)
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#33
In reply to #32

Re: Mounting Busbar For Ground, Outside Panel

10/19/2011 9:33 AM

Yeah. He was over the other day complaining about his right shoulder.............said it felt like a pulled muscle. He was treating it with whiskey.

Us manly men don't complain about a little pain, it just goes with the territory.

Since there are a few of us here that have more than a couple of grey hairs, I think I might start a thread about the importance of not ignoring a deep pain that comes along out of the blue.

We had discussed death on several occasions, and both of us agreed that however we go, we want it quick. So I'm glad for that. He had a drink mixed on his kitchen table, and it looks like he dropped like a rock in his hallway. Boom.

He was 75, not scared of dying, and he was getting tired. Those of us with any common sense have no desire whatsoever to live to 90 or 100. I know I don't.

Sh*t happens.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply Off Topic (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#35
In reply to #33

Re: Mounting Busbar For Ground, Outside Panel

10/20/2011 1:11 AM

Nah, we ain't gonna let you go until 110, after racking up 50,000 CR4 posts....

Sympathies to you and your friend's family, surely from all of us. Keep well.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Off Topic (Score 5)
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#36
In reply to #35

Re: Mounting Busbar For Ground, Outside Panel

10/20/2011 1:37 PM

Thanks Tornado.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply Off Topic (Score 5)
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#28
In reply to #20

Re: Mounting Busbar For Ground, Outside Panel

10/18/2011 4:36 PM

Excellent job sir!

Glad it worked out.

Thanks for coming back and posting the picture.

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#29
In reply to #28

Re: Mounting Busbar For Ground, Outside Panel

10/18/2011 5:54 PM

Thanks for setting me on the right track. The reason I was thinking of mounting a bar externally, is that there was no room inside. It wasn't easy, but it was easier than I thought it would be. I had every wire out.

That was the last step. I've already traced out every circuit in the house.....................................nothing was labeled when I moved in.

Now I can get back to wiring the kitchen so I can install cabinets.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#37
In reply to #20

Re: Mounting Busbar For Ground, Outside Panel

10/21/2011 11:00 PM

Sorry but it would never get past an inspection to BS7671 or Part P of the UK building regulations.

The UK regulations are getting to beyond the stage of a joke! 35 years as an industrial electrician and I'm not qualified to change the light fitting in my lounge unless I pay £420 to a council inspector to issue a certificate! Of course I could go for training and registration at a cost of near £1200 and issue my own certificate.

To hell with them the light fittings going in, what the eye doesn't see the heart doesn't grieve.

Living in a flat (apartment) I have to have an electrical PIR (Periodic Inspection Report) every 3 years. I think the 8 arm chandelier may be noticed.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#38
In reply to #37

Re: Mounting Busbar For Ground, Outside Panel

10/22/2011 10:46 AM

It's getting difficult to keep up with all of the rules and regulations over here too.

I'm not bothering with permits or inspections on my inside work. Technically it only has to be up to 1983 codes, but I'm going further than that on a lot of stuff.

I think the guy that built the house probably paid off the inspector when it was built. The house is solid, but as far as the electrical is concerned, I've found things that not only weren't up to code, but were actually dangerous.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#34

Re: Mounting Busbar For Ground, Outside Panel

10/20/2011 12:39 AM

Please use this type, can be placed / installed inside the same DB

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Register to Reply 38 comments