Grounding Fault at Cell Sites

10/18/2011 8:51 AM

Dears,


Please help me out on this. I've a grounding fault at my cell site. I installed a new IP55 cabinet that housed SDH radio and connected to -48Vdc system. The grounding cable connected to the cabinet is heating up once the SDH is powered. Ground (E) to -ve terminal voltage was reading 32Vdc. I checked between the ac conductors of ac supply (L1, L2, L3, N, E), and also between the dc part (-ve, +ve, E) all seems good (no short circuit and no leakage). All effort to identify why this is happening fail.


Let me state also that the site is being powered by 2 diesel generators and backed up by 2-battery banks of combined capacity of 1200Ah. All the installed teleco equipment, generators, tower and battery banks were tied to a common grounding.

thanks.

__________________
One good Thing deserves Another
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Grounding Fault at Cell sites

10/18/2011 8:57 AM

Is this a power-protective earth conductor or the earth condusctor for part of the transmission antenna's function, or both?

If the middle or latter, it would appear to be undersized.

If it is the first one, there is a sreious power supply problem that needs investigating and solving before someone gets hurt/killed.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Aug 2008
Location: Nigeria, West Africa (+1 GMT)
Posts: 46
#2
In reply to #1

Re: Grounding Fault at Cell sites

10/18/2011 9:06 AM

is the protective earth conductor, E.

__________________
One good Thing deserves Another
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Grounding Fault at Cell sites

10/18/2011 9:37 AM
  • Isolate the supply.
  • Open a link in the earth conductor.
  • Insert a voltmeter on a correct range in place of the link.
  • With no-one touching the equipment as a precaution, energise the equipment. Measure the voltage. De-energise the equipment, remove the voltmeter and close the above link.

What did the voltmeter say?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#4

Re: Grounding Fault at Cell Sites

10/18/2011 11:51 AM

Is the power supply supposed to be isolated? If you have an unintentional bond between the common power supply rail and station ground that may be causing this issue. A lot of manufacturers do this purposely to isolate any noise created by the SMPS.

If you are reading a voltage which is almost rail level between station ground and the negative side of the DC power supply, then the checks between the "dc part" should show a resistance value other than open or shorted. That should be spec'd for the installation.

The "ground to -ve" is 32VDC or -32VDC?

Register to Reply
Associate

Join Date: Aug 2008
Location: Nigeria, West Africa (+1 GMT)
Posts: 46
#5
In reply to #4

Re: Grounding Fault at Cell Sites

10/18/2011 11:56 AM

is 32Vdc.

__________________
One good Thing deserves Another
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#6
In reply to #5

Re: Grounding Fault at Cell Sites

10/18/2011 12:03 PM

You've got some sneaky ground issues there. I would check the specs for installation of that particular piece of equipment. I am assuming this issue appeared upon installation of the new equipment(?).

Are you using an unregulated external DC supply for the SDH? If so, I would check for compatibility i.e., grounding types.

Register to Reply
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#7

Re: Grounding Fault at Cell Sites

10/19/2011 5:02 AM

Someone has put a short between the -ve power rail of the SDH to the cabinet somewhere. This bit of wire will be getting very hot.

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Aug 2008
Location: Nigeria, West Africa (+1 GMT)
Posts: 46
#9
In reply to #7

Re: Grounding Fault at Cell Sites

10/20/2011 11:49 AM

Hi Randall

we were able to trace it and that was actually the cause.

many thanks to everyone!!

__________________
One good Thing deserves Another
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#10
In reply to #9

Re: Grounding Fault at Cell Sites

10/21/2011 11:19 PM

Crikey EnB!! You had a -48V to ground fault and a circuit breaker didn't trip or a fuse didn't, well, fuse. Protection is there to prevent conductors from "getting very hot". The protection obviously didn't work. The grounding system has not been correctly implemented (or designed) Under the condition you described and the fault that was discovered the "SDH" would not have turned "on" as you said. You are lucky that you did not start a fire. It is really sad that unqualified personnel are being used to perform installation tasks with equally ignorant supervision and a total lack of design. Keep up the bad work. It makes it easier for properly qualified folk to compete with cheap Charlies.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#8

Re: Grounding Fault at Cell Sites

10/20/2011 1:58 AM

You have a -48Vdc supply and you're measuring 32Vdc between the hot side and deck? This is plainly not right. Let's review what you should have there. Telecomms DC power system should be +ve ground. The bonding conductor should be from the +ve busbar of the power supply to the station's main earth and be the same size as the largest conductor inside the power supply. Typically 35 to 70 sqmm. You didn't say where you were obtaining your ground reference for the measurement you made. If a conductor is heating up it is conducting current. Did you measure the current? Do you have a DC clamp meter? If not stop right now. You are not equipped to perform any analysis (not easily anyhow). Does your SDH transmission equipment actually function? Was there any smoke? I note some serious deficiencies in the way you are going about this. For one, why was the SDH (radio, mux, OFTE... you didn't say which) powered up before checking or commissioning the DC power system? My guess here with the limited information supplied is that the 0Vdc return conductor is open circuit or not properly connected at either end. The ground conductor is acting as the return via some internal 0v to ground bond inside the SDH equipment. Ground bonding practices at this site seem dubious too. Try not to set fire to the site.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

cuba_pete (2); EnB (3); PWSlack (2); Randall (1); Wal (2)