i need a Electrical circuit diagram of digital synchronising relay to synchronise two parallel connected Generators....!!
Good Answers: 445
Re: Generator Synchronising Relay..!
10/19/2011 9:57 AM
What do you "need" this for, to understand how it works or to try and build your own?
Here's a verbal description: Three things need to match across the synchronization point; the source and system voltages, frequencies, and their phases. The outputs of those three comparators are "anded" and permission is given to the synchronizing breaker to close. I will leave the mundane details of making all this happen correctly to your engineering skills while navigating Google.
10/19/2011 1:41 PM
The relay does the comparison of two PT inputs i.e., Runinng PT & Bus PT.
Each PT should provide two phases (atleast) for the comparison.
Application: Synchronising Breaker to be selected (via Sync. Selector Switch) through which the BUS & Running PT will be selected.
Once the comparison i.e., Voltae,Frequency & Phase shift are performed, the relay permits the breaker to close.
For Circuit diagram click on th below link, SPMD10 relay (Page-3)
http://www.woodward.com/spmd10.aspx