Protection in AC Drives

10/20/2011 7:03 AM

In an AC Drive (VFD / Inverter ) short circuit protection is for the vfd input side or for vfd out put side ??

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Protection in AC Drives

10/20/2011 9:32 AM

Input. Otherwise, if the thing goes BANG then so will the upstream wiring.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Protection in AC Drives

10/20/2011 9:32 AM

The output side. Think of the VFD as a new "source" of motor power. If the motor or leads short or go to ground, the line side protection may not see it in time because the VFD is limiting the power that can flow into the circuit. So the VFD must protect the downstream systems from its own capacity.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Protection in AC Drives

10/20/2011 2:22 PM

Wait, now that I read PW Slack's response it dawns on me: there is a semantics issue here.

Are you referring to the motor Short Circuit protection FEATURE of the VFD, or are you referring to the Short Circuit protection that YOU MUST SUPPLY for the VFD installation? My answer would relate to the FEATURE in the VFD, PW Slack's answer would relate to what YOU MUST SUPPLY for the VFD installation.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Associate

Join Date: Nov 2008
Posts: 31
#4
In reply to #3

Re: Protection in AC Drives

10/21/2011 7:01 AM

Dear Jeraf

I am referring to the FEATURE IN VFD.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5
In reply to #4

Re: Protection in AC Drives

10/21/2011 11:02 AM

OK, but please realize, both statements are still true. The feature in the VFD is for the motor, it does not preclude your need for upstream short circuit protection FOR the VFD.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

JRaef (3); PWSlack (1); technology (1)