Electrical flash occured in dry type transformer which have folowing specs:
01- connection type- Dyn11
02- 1600kVA , 6.6/0.42kV , 140/2199A
03- Zsc = 6.28%
Phase and earth fault time Overcurrent protection of HV side operated.LV winding of C phase observed melted.HV winding of same phase seems open.Megger (performed at 1kV) results are as follows:
1. HV (6.6kV) Phase to Ground around 8000MΩ
2. LV (400V) Phase to Ground around 340MΩ
3. LV (400V) Phase to HV (6.6kV) Phase around 8000MΩ
Normal running current of transformer before fault occurrence was about :
· HV (6.6kV) side current -18 to 20A
· LV (400V) side current - 200A
Kindly comments against following queries:
01-What could be the probable causes of electrical flash or fault in transformer?
02-if we assume that Phase C HV winding became open first then What would be its effect on HV side current and LV side current and voltage?
03-If it is assumed that insulation failure happened on LV side first causing interturn fault then what would be its effect on HV side voltage and current?
04-what could be the probable causes of fault on HV winding?
05-what could be the probable causes of fault on LV winding?