Singel Pole vs. Double Pole MCB

10/22/2011 9:37 AM

I have seen people supplying single phase loads through a single pole MCB with phase going through MCB to the load and neutral connected directly to the load without any MCB. Is this technically OK and safe? should not we use a double pole MCB for single phase loads with phase and neutral both going through a two pole MCB to the load ?

In short, should we use MCB for neutral or should we fasten it directly to the load?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: singel pole Vs double pole MCB

10/22/2011 10:25 AM

Use of single pole CB only in line conductor is allowed and safe. Use of double pole CB for both line conductor and neutral conductor is also allowed and safe.

But the unsafe (not permitted) conditions are:

(1) Use single pole CB in neutral conductor

(2) Use fuse in neutral conductor, even though there is fuse in line conductor

(3) Use single pole switch or disconnector in neutral conductor

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 3)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#4
In reply to #1

Re: singel pole Vs double pole MCB

10/23/2011 7:49 AM

...or to use two separate MCB's, one for line and one for Neutral.....That is also unsafe.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#13
In reply to #4

Re: singel pole Vs double pole MCB

10/24/2011 4:00 PM

NO- Must be common trip. -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#14
In reply to #13

Re: singel pole Vs double pole MCB

10/24/2011 4:57 PM

I don't think you understand my English somehow!! I will repeat exactly what I wrote before, here:-

...or to use two separate MCB's, one for line and one for Neutral.....That is also unsafe.

Read the last few words again!!!

Now do you understand fully?

I was "adding" a comment of what was a list of unsafe procedures, they had forgotten this scenario.......

Try reading slower.

You were not alone either, someone else has trouble with English I noticed......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5
In reply to #1

Re: singel pole Vs double pole MCB

10/23/2011 10:23 AM

Msamad, while this is true in North America, it is not true in the rest of the world. They have different types of distribution systems, some of which REQUIRE switching of the Neutral.

coolyar, this means that your answer is dependent upon the type of power distribution system you have, as in IT, TT, TN, etc (don't use those literally, I am no expert on IEC systems. I'm going by memory and have no immediate resources available.)

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Aug 2007
Location: London England.
Posts: 583
Good Answers: 10
#6
In reply to #5

Re: single pole Vs double pole MCB

10/23/2011 3:09 PM

It is true that some installations require double contact switching, but not necessarily double pole MCB, However Earth leakage protection is always double pole

Bazzer

__________________
When I die I'd like to go peacefully in my sleep like my dad,not shouting and screaming like his passengers.
Register to Reply
Anonymous Poster #1
#2

Re: Singel Pole vs. Double Pole MCB

10/23/2011 6:12 AM

Dear one, ; we can use MCB for neutral wire . It will give better protection. But if we use only one MCB for phase it will also true but ht will not secure because if someone changes this phase and neutral ht will creat problem.

Register to Reply Off Topic (Score 5)
Power-User

Join Date: May 2008
Posts: 136
Good Answers: 2
#3

Re: Singel Pole vs. Double Pole MCB

10/23/2011 7:23 AM

Hi Coolyaar,

I completely agree with "msamad" in the priciples he've posed.... but what I'd like to add is that we usually use the single-pole MCB rather than double-pole one when there's no enough room in the main distribution box(as most of them are limited in size)..... bear in mind, every rule has exceptions.. when we deal with an MCB supplied with protection against Ground Fault(in this case, it's named RCD or RCCB and they're installed in bath rooms and other wet places) , hence you find such Circuit Breakers as Double-pole..

Hope this helps

__________________
Just live and .. Learn!!
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7

Re: Singel Pole vs. Double Pole MCB

10/23/2011 9:21 PM

It depends upon the type of your network. If the network is TN-C, then one must not break the neutral and thus shall go for a single pole MCB. In TN-S and in TT, then it is safe to go for SPN or DP MCBs.

Register to Reply
Active Contributor

Join Date: Jun 2008
Posts: 14
#8
In reply to #7

Re: Singel Pole vs. Double Pole MCB

10/24/2011 4:05 AM

Just to clarify, in what instance/situation would it be required to use DP? As from the replies above, there are restriction to use of protection on neutral so it would seem safer just to go with Single Pole.

Register to Reply
Member

Join Date: May 2008
Location: Kuala Lumpur
Posts: 6
#9
In reply to #8

Re: Singel Pole vs. Double Pole MCB

10/24/2011 4:55 AM

For electrical equipment located in hazardous area, the neutral must also trip when the phase trips. TN-C wiring method is also not allowed there.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10

Re: Singel Pole vs. Double Pole MCB

10/24/2011 6:52 AM

To wire the neutral through an overcurrent protection device falls outside British Standard 7671 and potentially could lead to electrocution/death.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#11

Re: Single Pole vs. Double Pole MCB

10/24/2011 7:47 AM

My experience with single pole RCBs (Residual current breakers) in a domestic setting, drove me up the wall. So if I ever have control over a future installation I will ensure that the breakers are double pole. The problem was that every time we were working on one of the circuits we turned off that breaker, but, if we inadvertently shorted earth and neutral, the main breaker would activate, and, turn off all the power.

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#12

Re: Singel Pole vs. Double Pole MCB

10/24/2011 2:04 PM

Please, PLEASE get a hold of a copy of your local electrical standards and regulations, many of the questions you ask here on CR4 you can answer yourself if you would just read these important documents.

__________________
jack of all trades
Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Ali18 (1); Andy Germany (2); Anonymous Poster (1); Bazzer Englander (1); Circuit Breaker (1); electricalexpert65 (1); jack of all trades (1); JRaef (1); Louwel (1); msamad (1); NAMINI (1); PWSlack (1); Randall (1)