Standard LT Motor Failure-VFD Driven

10/26/2011 5:16 AM

I come across a sudden failure of 3-phase 415V AC 75 kw induction motor which was vfd driven. Motor was in use for 8 month since commissioning. Motor failed due to inturn short.

Motor supplier shown the reason of non inverter duty class of motor. Understood that inverter duty class motor is recommended for VFD application. But i did not expect such rapid failure. There has to be some other reason also regarding motor manufacturing.

Which factors are critical while designing inverterduty motor? How does it differ from standard motor?

__________________
Stay foolish to learn..
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#1

Re: Standard LT Motor Failure-VFD Driven

10/26/2011 7:30 AM

In order for anyone to try and give answer to this question you pose, more info is needed. Such as; Motor load in amps & percent of fully loaded, percent of rpm running under load, ambient air temp where motor was being run. The more info you provide the easier it is to give feed back to your issue.

I have used non vector duty motors for ever and have not had many issues until you get into the lower RPM ranges. These areas can be a problem for these motors. I might add that even when using a non-vectored motor, using a higher rated insulation class will help as well. You should be able to read the insulation class off the motor you had go bad and posted that back with above info.

Register to Reply
Power-User

Join Date: Sep 2011
Location: Near the New Madrid Fault. USA
Posts: 269
Good Answers: 1
#2

Re: Standard LT Motor Failure-VFD Driven

10/26/2011 1:13 PM

Hi I agree with FIXITORELSE-- Heat is the #1 killer of motors, even the bearings can

loose there lube and overload or lock up a motor. Most have a 40 Deg.C rise over ambient but we had a new one fail at 4 months (Bearings)! The motors I deal with are 3 phase 460 Volt. I know motors come in a lot of different voltages but I have not seen a 415V one, if you are operating a 460 V motor at 415 Volts it may be a problem if it can not develop the HP it needs. A drive just changes the Frequency thus RPM. The turn to turn short is a fairly common failure and a VFD will "fault" out if anything is wrong with the motor circuit. Also if a motor sits in storage or not running for years the bearings may fail sooner than you think. Inverter duty motors generally have better insulation on the windings and steel in the core and rotor.

__________________
It's not Rocket Science
Register to Reply
8
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Standard LT Motor Failure-VFD Driven

10/26/2011 5:03 PM

The issue of Standing Wave generation damaging motor windings, typically in the first turns, is very real and can be very rapid. If you are unaware of this issue, the quick explanation is as follows:

Because of the high speed switching of the transistors used in the VFD output, the cables going to the motor experience a form of capacitive coupling that creates voltage pulses. As these voltage pulses travel the length of the cable at various harmonic frequencies, some cancel each other out but others add together, then get reflected back by the motor, where they continue to interact back and forth, building all along the way. At some point the pulse potential gets to be extremely high, as in 2-3 times the line voltage. In older non-inverter designed motors, the insulation was often 1.5 - 2X the line voltage, which is now inadequate. So the built-up pulses eventually punch through the insulation, usually at the first weak point, the first turn in the stator winding. The phenomenon gets progressively worse with distance from the VFD to the motor because the pulses can rise faster with more capacitive coupling, but I have seen damage on motors installed within 25ft. There is no guaranteed distance that can be used, short of possibly mounting the VFD directly to the motor, which is done in some cases.

If you do a search on "Standing Waves in AC motors" you will be able to study this in more depth, and see the various mitigation strategies. However a simple one to implement on an older existing motor is to use a low cost Motor Lead Filter, available from most of the people who sell Line Reactors and EMI filters for the line side of the VFD.

The reason some people never see this issue is mostly a matter of luck, or the fact that they are unaware of a pre-installed filter. But also here in North America some people never experience it because it is not as big an issue on 240V motors and below, simply because the magnitude of the spikes created by the standing waves is less likely to exceed the winding insulation rating, because most of the time the motor mfrs use the same insulation for 480V motors as they do for 240V.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 8)
4
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#4
In reply to #3

Re: Standard LT Motor Failure-VFD Driven

10/27/2011 8:50 AM

Absolutely right, GA. I'd just clarify that the rapid switching of the transistors will remain the same, regardless of what speed you run your drive, it is the carrier frequency, someting ranging from 4 to 15 KHz depending on the drive and your settings.

The same phenomenon that you mention (capacitive coupling) causes another undesirable effect: micro-electro abrasion, which wears out the bearings in no time, due to arc discharges between the rotor shaft and the motor shell, passing thru the bearing, if you see these bearings under the microscope, you'll see a lot of pits and cracks, the solution is to use either insulated bearings or connect a brush from the shell to the shaft.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply Good Answer (Score 4)
Power-User

Join Date: Sep 2011
Location: Near the New Madrid Fault. USA
Posts: 269
Good Answers: 1
#5
In reply to #4

Re: Standard LT Motor Failure-VFD Driven

10/27/2011 9:22 AM

Everyone is on the Money GA's..and just FYI we have hundreds of motors on VFD's at this plant and have only one documented "EDM" failure and it was not a run to failure.

We found it with Ultrasonic testing.The Drive end bearing had visible "Fluting". The VFD was not grounded properly to the motor but the motor was grounded to our grounding grid and building steel. Load side Reactors, proper grounding, shaft brushing seals (or clamp on) will stop all that Electrical Discharge Machining.

__________________
It's not Rocket Science
Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#6
In reply to #5

Re: Standard LT Motor Failure-VFD Driven

10/27/2011 1:34 PM

Correct, and I bet you're following manufacturer's recommendations, standard practices an all codes, just that you missed that one instalation in particular.

But it becomes much more apparent in other scenarios, for example some electric vehicles, they use AC servomotors ran by a high-end VFD. and the bearings are among the most prone to fail parts, much more than the windings.

In my experience working at one major manufacturer of servo motors (almost a monopoly), "EDM" and electrical noise were killing most of them. Wait a minute you may say, electrical noise?... Yup, the bearings featured a built-in pulse coder susceptible to fail due to lose connections on the power leads at the test stations.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Power-User

Join Date: Sep 2011
Location: Near the New Madrid Fault. USA
Posts: 269
Good Answers: 1
#7
In reply to #6

Re: Standard LT Motor Failure-VFD Driven

10/27/2011 2:17 PM

Me gusto mucho, bueno trabajo amigo.

__________________
It's not Rocket Science
Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#9
In reply to #7

Re: Standard LT Motor Failure-VFD Driven

10/28/2011 8:17 AM

Gracias, compadre !

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Participant

Join Date: Oct 2011
Posts: 1
#8

Re: Standard LT Motor Failure-VFD Driven

10/28/2011 6:04 AM

Kindly check the reduction in RPM done by reducing frequency using VFD . IF it is reduced below say 50 % of rated RPM of motor . The cooling fan speed reduces accordingly Thus motor is not cooled by the fan sufficiently as it would have done when running at rated speed . Hence overheating of motor and failuer Hope this clarifies your query As motor used by you might not have forced fan cooling arrangement

In VFD suitable motors

1. Forced fan cooling is provided . Thus even motor runs at lower RPM than rated for long period , the cooling of motor is done by Fan which is run by another small motor

2. The insulation of Motor winding is done by Vaccum Pressure Impregnation ( VPI ) Method as against normal Dip method. Thus Insulation coating is uniform across the entire winding hence points of failuer are reduced drastically Hence better thermal performance of Motor.

However practically if Motor is VPI treated it may not fail if RPM reduction is restricated to say 10 to 15 % of Rated RPM.

Best thing is if you are planning to run motor with VFD kindly ask Motor suitable for VFD from manufacturer.

Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: Oct 2008
Location: Surat, India.
Posts: 14
#10
In reply to #8

Re: Standard LT Motor Failure-VFD Driven

10/29/2011 2:33 AM

Thank you very much to all.

__________________
Stay foolish to learn..
Register to Reply
2
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#11

Re: Standard LT Motor Failure-VFD Driven

11/02/2011 1:53 PM

Dear Substation15,

The Cooling Aspect of Motor especially while running at minimum or less speed, Bearing Insulation or Usage of INSULATED BEARING, Perfect Earthing, Hormonic Filters, Distance between the Motor and the Inverter are the important factors involved.

DHAYANANDHAN.S

Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Jun 2014
Posts: 15
#12
In reply to #11

Re: Standard LT Motor Failure-VFD Driven

06/08/2014 1:26 AM

I agree with the facts of failure with all above. We have a strange case. Since 3 years, We have installed-8X150 kW pump-motors with 6-pulse Siemens-VFD on an exclusive 2500 kVA transformer-of-course-missed out to install HARMONIC filter. Frequent failure of VFD-control cards are reported. We have taken care about all except harmonic filters. . The I Thd is 45% and V-Thd is 3.5%. Kindly suggest remedies and bad effects of not installing harmonic filters. Management says-that nothing happened except control-card failures and why expensive ACTIVE HARMONIC FILTERS ARE Needed?

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#13
In reply to #12

Re: Standard LT Motor Failure-VFD Driven

06/09/2014 5:01 PM
  • I agree with the facts of failure with all above. We have a strange case. Since 3 years, We have installed-8X150 kW pump-motors with 6-pulse Siemens-VFD on an exclusive 2500 kVA transformer-of-course-missed out to install HARMONIC filter. Frequent failure of VFD-control cards are reported. We have taken care about all except harmonic filters. . The I Thd is 45% and V-Thd is 3.5%. Kindly suggest remedies and bad effects of not installing harmonic filters. Management says-that nothing happened except control-card failures and why expensive ACTIVE HARMONIC FILTERS ARE Needed?

It may have been better to start a new thread on this, but too late now.

I tend to agree with your management on this one, it's unlikely that the control board failures are the direct result of excessive harmonics. The control boards are powered separately, usually off of the DC bus with a DC-DC power converter, but sometimes off of the AC side with an AC-DC switched mode power supply board. Either way, the control voltage going to the board is going to be isolated from the mains.

Control board failure causes tend to fall into two main categories: environmental and electrical noise related.

If the drives are getting too hot inside their enclosures, it is usually the PC boards that fail first, because the drives themselves often have protection schemes to automatically lower the motor speed to protect the transistors from over heating, but if the ambient air is too high, the boards cook anyway. I have also seen cases of air contaminants such as H2S causing corrosion and failure on boards. As I recall, Siemens only offers what is called "conformal coating" of the PC boards as an option.

Improper shielding (screening) of control wiring is a good way to allow introduction of common mode electrical noise to get into the PC board circuits. Most have filtering to help prevent that, but over time, repeated attacks eventually cause the filtering to wear out and fail, then the board circuits are quick to follow. If you are using shielded control cables, make sure that only ONE END is grounded (earthed). That is a common problem.

Good luck.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2014
Posts: 15
#14
In reply to #13

Re: Standard LT Motor Failure-VFD Driven

06/18/2014 12:33 AM

Great feeling to read through the message/content. I am examining the card failure and will ensure --environmental/noise issues. Your mention that Shielded control cables being grounded at one ned-i feel is very precise for me to examine the site issues. Thank you and my best regards.

Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Arhaddas (1); dhayanandhan (1); fixitorelse (1); JRaef (2); Rockyscience (3); srgovind (2); Substation 15 (1); Yahlasit (3)