Please can any one help me on this.

On my calculation of a small retail shop the load is found to be 10kW and another for 20kW.

What will be the rating of the isolator to be provided for both the cases. is 63A(3ph) ok for both. On future the retail shop will install DB and will have lighting and power circuit of 10A, 16A and max 32A.

Can any one please share your expereince of this isolator rating in both the cases considering descrimination

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Incomer Rating of a small retail shop

10/27/2011 8:50 AM

Will the forum know the supply voltage?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Sep 2011
Posts: 11
#3
In reply to #1

Re: Incomer Rating of a small retail shop

10/27/2011 10:01 AM

400v is supply voltage. Thanks

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Incomer Rating of a Small Retail Shop

10/27/2011 9:02 AM

You really should have paid attention in class.

Or, maybe you should become an apprentice and study under an electrician with some experience, before striking out on your own.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: Incomer Rating of a Small Retail Shop

10/27/2011 9:07 PM

Have a look at his previous posts……

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Active Contributor

Join Date: Sep 2011
Posts: 11
#5

Re: Incomer Rating of a Small Retail Shop

10/28/2011 4:48 AM

Dear Friends,

Be professional in comments

Thanks

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#6

Re: Incomer Rating of a Small Retail Shop

10/28/2011 11:17 PM

Contact your utility and ask them to give a list of standard supply ratings normally given by them like-1 ph-15A,30A,60A,3ph-30A,60A,100A,160A,11kV-100kVa,160kVa and so on and select the one which meets your demand. Or give them a load schedule of your premises and ask them to provide a suitable supply based on acceptable diversity and load factors.