Generator

10/30/2011 11:04 PM

Hi Guys

I have a plant that runs on American voltage 3phase 220 50Hz[line 1 to line 2], but the generator I have is British voltage 3 phase 50Hz380 [line 1 to line 2] at a capacity load of 200 kva. However I decided to re-arrange the output terminals of HIGH WYE 3 phase, 380volts to SERIES DELTA 3 phase 220volts.

A. What are the implications concerns even thou I have tried and its works good [advantage and dis-advantages]

B. Will the capacity of the generator increase or decrease

C. What are the formula for both increase in KVA and decrease in kva

Thanks for the usual cooperation's, waiting for your response

Regards

Aishaamadumariama

Register to Reply
Pathfinder Tags: AAM
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Generator

10/31/2011 1:51 AM

If both ends of the windings are brought out as six separate connections, this should give the option of connecting them in star (380V + neutral) or delta (220V without neutral). (If there are 12 connections, that would give some more series/parallel choices). The total KW should be the same.

50Hz is not a normal U.S. frequency; nor is 220V a normal distribution voltage, although there are colloquial references to it.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#2

Re: Generator

10/31/2011 3:10 AM

Rearranging the connections from a star to delta only changes the output configuration so your total KVA rating stays the same. Volts are volts regardless of how you got them.

American voltage is typically 120/240 60Hz For single phase and the most common three phase voltages are 120/208, 120/208/240, 240, or 277/480 for most applications.

There are also a number of less common voltage configurations as well but they tend to be more specific application.

Register to Reply
Register to Reply 2 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!

Previous in Forum: Mini Project - Maintenance Based on Vibration Measurement & Analysis   Next in Forum: final year project

Advertisement