Circuit Breaker Rating

11/05/2011 4:43 PM

hi everbody, i m just look at MCB rating and found that the there is no any proper series or order between them like 6 A, 10 A, 13 A, 16 A, 20 A, 25 A, 32 A, 40 A, 50 A, 63 A, 80 A and 100A why these rating like this? why they are not in proper series?... is any specific reason for such type of rating.. plz guide... and thanks in advance

__________________
Parteek Gola
Register to Reply
Pathfinder Tags: Circuit breaker rating
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Circuit breaker rating..

11/05/2011 4:56 PM

So what do you think would be a proper ordering? Arithmetic or geometric progression, or something else? 400 different sizes from 1 to 400 amps?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#2

Re: Circuit Breaker Rating

11/06/2011 1:07 AM

These ratings may have some relationship with standard sizes of copper conductors used in power cables. for instance 63A for 16mm^2 wire and so on.

__________________
pnaban
Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Circuit Breaker Rating

11/06/2011 8:45 AM

STANDARDISATION, I would say!

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4
In reply to #3

Re: Circuit Breaker Rating

11/06/2011 9:30 AM

Yes.Standard sizes of protective devices should correspond to current ratings of standardised cable sizes,otherwise it is meaningless. Refer BS 7671 relationship between Iz,Ib,In in which the load current,cable size(current rating) and size of PD(current rating) are interrelated. Compare the rated current of standard size cables- 1,1.5,2.5,4,6,10,15, 25, 35mm^2 etc with that of rated current of PDs.

__________________
pnaban
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2011
Location: Haridwar (India)
Posts: 18
#6
In reply to #4

Re: Circuit Breaker Rating

11/06/2011 1:39 PM

thanks a lot sir...

__________________
Parteek Gola
Register to Reply Off Topic (Score 5)
3
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5

Re: Circuit Breaker Rating

11/06/2011 10:45 AM

The ratings are generally as per Renard Series (#5 or #10). Please read this Wiki page : http://en.wikipedia.org/wiki/Preferred_number

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Good Answer (Score 3)
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); kvsridhar (1); pgola4u (1); pnaban (2); Tornado (1)

Previous in Forum: Grounding Topics   Next in Forum: Power Factor Measurement

Advertisement