Electrical Insulation Resistance Test

11/06/2011 12:37 AM

Dear sir,

I was doing the Insulation Resistance test (1000V Megger)for Main LT switch board, but Insulation value is coming around 100Mohms.But Consultant rejected the test due to low Insulation .Kindly let us know what is the Min.Insulation resistance value as per IS/IEC .

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Electrical Insulation Resistance test

11/06/2011 12:47 AM

Get your own copy of the specifications that you claim to be testing to.

Your ignorance of electronics is inexcusable for someone who, apparently, is taking money from other people to fabricate and test electrical devices.

Please tell me I'm wrong.

Register to Reply Score 1 for Good Answer
Commentator

Join Date: May 2011
Posts: 84
Good Answers: 1
#2

Re: Electrical Insulation Resistance test

11/06/2011 4:24 AM

what is the voltage of your LT board?

if it is 415 V then accepted value is 1.415 Mohm.

standard accepts kV+1 Mohm IR value for each voltage level.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5
In reply to #2

Re: Electrical Insulation Resistance test

11/07/2011 12:01 AM

According to VDE it should be 1000ohms/kV. What is the recommended test voltage?.

__________________
pnaban
Register to Reply Score 2 for Off Topic
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Electrical Insulation Resistance test

11/06/2011 8:42 AM

Change your consultant. As per Indian Electricity Rules. 1956, Rule No. 48 (i), the minimum insultaion resistance for 415V installtion, with a test voltage of 500V DC, is only one mega-ohm.

Register to Reply
Participant

Join Date: Nov 2011
Posts: 2
#4

Re: Electrical Insulation Resistance Test

11/06/2011 10:41 PM

Dear Mr

As per IEC 1 Mega Ohms /1 KV is ok

Register to Reply
Participant

Join Date: Oct 2011
Posts: 2
#6

Re: Electrical Insulation Resistance Test

11/07/2011 10:25 AM

100 MΩ IS MORE THEN ENOUGH.FOR 415 V LT POWER 1MΩ IS RECOMENDED VALUE BY IR RULES.YOUR CONSULTANT IS WRONG.

Register to Reply
Power-User

Join Date: Dec 2010
Posts: 166
Good Answers: 4
#7

Re: Electrical Insulation Resistance Test

11/07/2011 12:39 PM

The specification is "The Specification". If their expectations are unrealistic, then refer them to "Somebody Else".

Register to Reply
Associate

Join Date: Jul 2007
Posts: 26
Good Answers: 1
#8

Re: Electrical Insulation Resistance Test

11/07/2011 10:44 PM

Good insulation resistance . Don't have to worry at all . ( Operating voltage divided by 1000 ) + 1 megohms is the thumbrule . Soo 100 mohms is very good .

Register to Reply
Active Contributor

Join Date: Sep 2010
Posts: 17
#9

Re: Electrical Insulation Resistance Test

11/08/2011 3:34 AM

if you are working in UAE, then most consultants prefer a perfectly insulated wire/ busbar i.e >999Mohm.

even though IEC & British Standards mention a insulation resistance of 1000ohm/volt (IEC) & >=1Mohm (BS) for a LV system using a test voltage of 500V or 1000V dc , the consultants still prefer the highest value shown in the megger which is >999Mohm.

using a megger-insulation-tester

Register to Reply
Member

Join Date: Sep 2011
Location: UAE
Posts: 7
#10

Re: Electrical Insulation Resistance Test

11/13/2011 11:12 AM

Hi every1... I have a similar question.

What is the IR value that is expected in LT power cable(1100 V), when tested at site before laying the same. Is the value universal? Please give the separate values for XLPE and PVC cables, 500m and 1000m each.

Many thanks in advance....

Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Alwin Paul (1); electricalexpert65 (1); Gazu (1); harrybrown (1); lyn (1); muditmah (1); murugavelt (1); pnaban (1); SCSharma17 (1); Voltamps (1)

Previous in Forum: Power Factor Measurement   Next in Forum: Elctrical Grounding/Earthing

Advertisement