Neutral Earthing at Load End

11/08/2011 8:02 AM

can we earth neutral of cable seperately at load end, is there any effect on Asymmetrical current component and fault current?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: Neutral Earthing at Load End

11/08/2011 8:47 AM

Neutral MUST always be earthed only and ONLY at the source, nowhere else.

Register to Reply
Associate

Join Date: Nov 2011
Location: mumbai
Posts: 28
#5
In reply to #1

Re: Neutral Earthing at Load End

11/09/2011 12:47 AM

is there any standard formula for deciding earth conductor size.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6
In reply to #5

Re: Neutral Earthing at Load End

11/09/2011 1:37 AM

S = I Root 't' / K

S = Earthing Conductor Cross Section in sq.mm

I = Fault Current in Amperes

t = Duration of fault, in seconds

K = Constant, depending upon the material of conductor, fault duration, etc. (Refer to IS 3043 for the values of these constants)

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #5

Re: Neutral Earthing at Load End

11/09/2011 11:57 AM

British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Dec 2011
Posts: 13
#10
In reply to #1

Re: Neutral Earthing at Load End

12/05/2011 2:03 AM

Your answer is wrong, this is mentioned in articles below. With respect beware replying if you do not have the correct answer it may confuse the poster.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#11
In reply to #10

Re: Neutral Earthing at Load End

12/05/2011 2:33 AM

dbman

Which articles? Nothing is there in your post.

We are all very curious to learn from you especially since you seem very sure of yourself. i hope you will ensure that your future posts will be complete.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#2

Re: Neutral Earthing at Load End

11/08/2011 10:06 AM

Boy! Are you in luck!

This was just covered recently...right here on CR4! How much more on-topic and essential can you get than the forum of CR4?

http://cr4.globalspec.com/thread/73442/Grounding-Topics

Thank you, God, for CR4. (p.s., could you please include some instructions on the search function?) If it's not asking too much...

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: Neutral Earthing at Load End

11/08/2011 10:57 AM

Actually, thanks to Wareagle !!!

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#7
In reply to #3

Re: Neutral Earthing at Load End

11/09/2011 10:09 AM

That, too...

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Neutral Earthing at Load End

11/08/2011 11:54 AM

Although it can be, there is no earthly reason [] why it should be.

Please refer to British Standard 7671.

There is a page in Wikipedia on earthing systems that shows the methods of earthing and the reasoning behind them.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Neutral Earthing at Load End

11/09/2011 12:48 PM

Failing that, consult a qualified electrician.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply