ELECTRIAL AC SLIP RING MOTOR

11/15/2011 11:54 AM

I M FACING PROBLEM OF FREQUENT FAILURE SLIPRING OF 800HP 415V 50HZ INDUCTION MOTOR. TWO TIMES I REPLACED SLIPRING BY NEW BUT AFTER RUNNING FOR 3 TO 6 MONTH SAME MOTOR SLIPRING GOT HEAVY SPARK AT STARTING & GOT DAMAGED. I CHECKED ROTOR WINDING BY MEGGER, OHM BY MULTIMETER IT FOUND OK. WE REDUCING ROTOR RESISTANCE BY DEEPING PLATES IN CAUSTIC SODA WATER. IN OUR PLANT MORE THAN 10 AC SLIPRING MOTOR, ALL ARE RUNNING WITHOUT TROUBLE. KINDLY ADVISE.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: ELECTRIAL AC SLIP RING MOTOR

11/15/2011 12:15 PM

Not enough information, but a first guess would be that you have too little resistance at startup.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Active Contributor

Join Date: Nov 2011
Posts: 11
#2
In reply to #1

Re: ELECTRIAL AC SLIP RING MOTOR

11/15/2011 12:26 PM

KINDLY TELL WHAT FURTHER DETAILS YOU NEED, BUT YOUR SUGGETION IS VALUABLE.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: ELECTRIAL AC SLIP RING MOTOR

11/15/2011 12:56 PM

Let's start with this: Do you understand how a slip ring induction motor works? If you do, then what is the nature of the load and how are you accelerating it? Liquid Resistance? Stepped resistance? If stepped, how many steps and how much resistance in each step? If you don't know all of this, then has anyone done a starting analysis comparing the necessary accelerating torque of the load and the motor torque/speed curves of the motor with the various rotor circuit resistance amounts?

And please stop using your Caps Lock. I know it might make it easier for you to not have to worry about proper capitalization, but it makes it more difficult for people to read it. Reading types text is more than just looking at letters, we also look at the shapes of words in order to process known words faster. When you use all caps, if forces the reader's brain to slow down and r e a d e a c h l e t t e r s e p a r a t e l y, which I for one find frustrating. Plus it is considered the equivalent of shouting and deemed rude.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Active Contributor

Join Date: Nov 2011
Posts: 11
#4
In reply to #3

Re: ELECTRIAL AC SLIP RING MOTOR

11/15/2011 1:29 PM

Sorry for caps lock writing, I know very well of slipring induction motor. We are using 800 hp slipring motor for running ribbed bar(using for civil construction) rolling mill of 14". Rotor is added with water resistance using ss plates dipped in caustic soda water. When motor starts plates are small deeped in water and then we graually start deeping plates by screw operated handle, after we reach to full speed & reduce starting current, we short all water resistance by copper short link.

Register to Reply
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: ELECTRIAL AC SLIP RING MOTOR

11/15/2011 3:09 PM

If the flashover occurs on the initial start it sounds a classic case of incorrect brush grades linked with insufficient cleaning. You really have to have a rigorous cleaning regime. Following similar problems in a steel plant, new cleaning methods were used and before start up a series of tests were run.

Disconnect the rotor from the rings and remove all brushes.
IR test between each of the rings and each ring to earth.
Disconnect the cable to the liquid starter.
IR test between the sets of brush holders and to earth.

It takes time but it's quicker than changing the rings and brush gear when thet've flashed over.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#6

Re: ELECTRIAL AC SLIP RING MOTOR

11/26/2011 12:43 AM

You are using a LRS.Ok.Now what is the material of slip ring? copper, Cupro nickel?Observe whether solder run out is there.Best solution is to use a slip ring motor with automatic brush lifting and short circuiting arrangement where the slip ring come in only during starting.The advantage of slipring motor at starting and running like cage is obtained.Check your motor carefully.many times the leads coming to slip ring gets damaged due to sudden jerks in starting or stopping.by the what is the application? how soon u take to cut off the resistor? is it motorised?

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#7

Re: ELECTRIAL AC SLIP RING MOTOR

01/16/2014 9:59 AM

Dear Mr.AshokTakali,

Pl. check for the following.

1. Grade of the Carbon Brushes and its hardness.

2. Quality of Slip Ring whether it is commercial copper ir IE grade.

3. What is the starting current and how long that is How Many Seconds the motor takes to accelerate to full speed.? Here the GD^2 Value of the revolving equipment comes in to picture.

4. Whether the Starting Torque developed is as per the design,?

5.Whether the Motor is started against Load or the Motor is started and then load is put.? If it is started against load, then additional resistance is required in the starter, while starting only.

Pl.post the information, what was the problem, and solution arrived.

DHAYANANDHAN.S

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#8
In reply to #7

Re: ELECTRIAL AC SLIP RING MOTOR

01/17/2014 8:38 AM

In slip ring motor the starting current and starting torque are dependent on external resistance and you can have a starting torque as high and equal to POT.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Register to Reply 8 comments