Space Heater Provision in LV Electrical Panel

11/15/2011 11:38 PM

Dear SIr,

Kindly let us know the location of the space heater & thermostat in an Main Power distibution electrical Panel.

Regards

Murali

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Space heater provision in LV Electrical panel

11/16/2011 12:22 AM

The heater should be located near the bottom, on whichever side has more space below any heat-sensitive components. The thermostat sensor should also be near the bottom, but at the opposite side from the heater. This configuration will induce a convection loop of warmer air rising from the heater, falling down on the other side, and then passing across the sensor.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#2

Re: Space heater provision in LV Electrical panel

11/16/2011 12:55 AM

3 best possibilities.

1-> heater bottom, thermostat top

Reason: heater at the bottom to heat the cool air located at the bottom of the enclosure & thermostat at the top to monitor the temperature as by natural convection hot air will move vertically.

2-> heater bottom, thermostat bottom (opposite sides)

Reason:heater at the bottom to heat the cool air located at the bottom &thermostat at the bottom so that it is shielded from radiated heat & also it will monitor the lower end of the panel

3-> heater bottom, thermostat top (opposite sides)

Reason: Same as 1

also take care that there are no tripping devices (MCB, MCCB) nearby the heater. it may cause unnecessary tripping due to the external heat.

__________________
shamith gambhir, electrical engineer
Register to Reply Score 1 for Good Answer
Register to Reply 2 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!

Previous in Forum: turbine vibaritions   Next in Forum: Heat Shrink Sleeve for Copper Bus Bar

Advertisement