2 wire RTD w/ 4 wire transmitter

11/16/2011 11:11 AM

Hello all, I am trying to wire in a 2 wire PT100 RTD to a 4 wire transmitter (rosemount 148) and having difficulty getting it right. Has anyone had experience with this and how to wire it? Thanks for your patience with this newbie.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator
Venezuela - Member - New Member

Join Date: Aug 2010
Location: Venezuela
Posts: 88
Good Answers: 5
#1

Re: 2 wire RTD w/ 4 wire transmitter

11/16/2011 12:45 PM

Hi sparktest,

Regards

JP

__________________
Instruments-guy-SAV
Register to Reply
Participant

Join Date: Nov 2011
Posts: 4
#2
In reply to #1

Re: 2 wire RTD w/ 4 wire transmitter

11/16/2011 1:23 PM

Thanks, but im looking at the same thing and it doesnt work that way. I tried to connect a three wire and still nothing. Although I pulled a four wire RTD from another process and presto everything worked fine. I suppose I should just get a four wire RTD and be done with it unless there is something obvious Im missing.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #2

Re: 2 wire RTD w/ 4 wire transmitter

11/17/2011 3:24 AM

Join terminals 1 and 2 with a wire link. Join wires 3 and 4 with a wire link. Connect the 2-wire RTD across terminals 2 and 3. What happens?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#3

Re: 2 wire RTD w/ 4 wire transmitter

11/16/2011 1:50 PM

"and it doesnt work that way."

Please tell us exactly, what didn't work.

What are the symptoms of it not working?

Register to Reply
Participant

Join Date: Nov 2011
Posts: 4
#4
In reply to #3

Re: 2 wire RTD w/ 4 wire transmitter

11/16/2011 2:46 PM

Sorry for the lack of details. With the 2 wire RTD wired im getting 21.8 mA back to the DCS (delta V) and no output change based on the simulated temp..this is the same reading with no RTD landed. Same scenario with the 3 wire but with the 4 wire it reads an accurate temp. on a meter and and back to the DCS. Im wondering if this 148 transmitter isnt working properly...

Register to Reply
Commentator
Venezuela - Member - New Member

Join Date: Aug 2010
Location: Venezuela
Posts: 88
Good Answers: 5
#5
In reply to #4

Re: 2 wire RTD w/ 4 wire transmitter

11/16/2011 4:45 PM

Sparktest,

I have never worked with a rosemount transmitter 148, but I can recommend that you check the configuration of this equipment(148). I do not know if this instrument automatically detects the type of connection made with the RTD wires, ie if it is 2 wire 3 wire or 4 wire RTDs.

Acording your first post, you are checking a transmitter 148 selected originally for use a 4 wire RTD sensor, Now, you are putting two and three wires RTD, please check the configuration in the transmitter, maybe that is the problem.

Regards

JP

__________________
Instruments-guy-SAV
Register to Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#6

Re: 2 wire RTD w/ 4 wire transmitter

11/16/2011 6:26 PM

I doubt the transmitter autosenses the RTD configuration. The transmitter is likely configured as a 4 wire RTD transmitter, and will only produce a valid reading when a 4 wire RTD (or 4 wire resistance) is connected to it. Otherwise it goes to fault condition.

Page 1257 (paper) or page 1277 (pdf) of Mr. Kuphaldt's Lessons in Industrial Instrumentation book
illustrates the operating basics of a 4 wire RTD analog input.

If the any of the 4 sensor wires are missing, the voltage cannot be sensed, the transmitter detects an open circuit and responds by driving the output to a fault condition, typically up-scale burnout; in this case, 21.8mA.

The transmitter's configuration needs to be changed to 2 wire RTD, or you can add two additional copper wires as shown in the wiring illustration to create a 4 wire RTD.

Register to Reply
Commentator

Join Date: Dec 2007
Location: texas
Posts: 92
Good Answers: 8
#7

Re: 2 wire RTD w/ 4 wire transmitter

11/16/2011 7:00 PM

Hi,

These type of transmitters do not auto detect the type of temperature elements connected to them.

Sounds like your temperature transmitter doesn't know what type of temperature element you are using.

Use a communicator to make sure that the transmitter is set up for 2 wire PT 100(sounds like it's set up for 4 wire)

After you set it up for the correct temperature element connect the 2 wire RTD and see if you get a good transmitter output.

If you still don't get a good output then either ohm out the 2 wire RTD to make sure it's good or use the 4 wire RTD as a 2 wire RTD by connecting the two common legs together.

If the transmitter still doesn't work then invest on 4wire RTD just joking!

Hope this helps

Thanks

__________________
"The older I get -The better I was"
Register to Reply
Power-User
Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - New Member Technical Fields - Technical Writing - New Member Technical Fields - Education - New Member Fans of Old Computers - Apple II -

Join Date: Sep 2011
Location: Bellingham, WA
Posts: 191
Good Answers: 46
#9

Re: 2 wire RTD w/ 4 wire transmitter

11/17/2011 8:29 AM

Hi Sparktest,

The subject of how to connect RTDs to RTD transmitters of differing wire count can be confusing. Here is a screenshot of the connections you'll need:

If you need more commentary on this, read section 21.3.5 "Proper RTD sensor Connections" and you'll be sure to find the information you're looking for. The "incorrect" wiring scheme shown will function, but it won't be as accurate as the "correct" scheme.

- Tony

__________________
They call me "lightning" when wielding a hammer, because I never strike twice in the same place
Register to Reply Score 1 for Good Answer
Participant

Join Date: Nov 2011
Posts: 4
#10
In reply to #9

Re: 2 wire RTD w/ 4 wire transmitter

11/17/2011 11:38 AM

Thank you for sharing that information and the link to your book, what a great piece of work!

Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Instruments-guy-SAV (2); Iris (2); PWSlack (1); sparktest (3); tonykuphaldt (1); wrenchpuller (1)