Anonymous Poster #1

Generator Cap. Comp.

11/18/2011 5:25 AM

im computing generator current capicity with rated 300KW,3ph, 230V,80%pf. and come-up with an ans. of 941A.. is this the line current? how can i get the current per phase?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: generator cap. comp.

11/18/2011 5:28 AM

Is 230V phase-to-phase or phase-to-neutral?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Participant

Join Date: Nov 2011
Posts: 1
#3
In reply to #1

Re: generator cap. comp.

11/21/2011 12:48 AM

230v phase to phase, 110 phase to neutral..

Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Generator Cap. Comp.

11/18/2011 1:58 PM

300KVA
230V Ph - Ph @.8Pf = 602A
230V Ph - N @.8Pf = 346A

If you want to know how to work it out get your books out.