Parallel Operation of Transformers

11/21/2011 8:32 AM

Dear friends,

We do have two 66/33/15Kv transformers with a capacity of 12/16MVA (ONAN/ONAF) each, which can not operate in parallel due to greater impedance difference in the 15Kv side.

So, can the transformers operate parallely in the 33Kv side only, but with separate busbar for the 15Kv side?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Parallel Operation of Transformers

11/21/2011 11:48 AM

If they were fed from the same 33kV source and not connected to the same downstream 15kV load, then they would not be operating in parallel; each transformer would not know of the other's existence, so to speak.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Sep 2011
Posts: 4
#3
In reply to #1

Re: Parallel Operation of Transformers

11/22/2011 12:23 AM

To make the question clear, the transformers are fed from a common 66KV busbar and our plan is to make them operate parallel only in the 33Kv side, but isolate the 15Kv bubar so that they will operate separately in the 15Kv side.

Register to Reply
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#4
In reply to #3

Re: Parallel Operation of Transformers

11/22/2011 2:14 AM

As far as I understand you a two transformers, 3 windings each, 66K k/33 kV/15 kV and you want to paralell them on the 66/33 kV but no parallel on the 15 kV side because of the impedance.

Overall, if the conditions are good for connecting them in parallel only between 66 kV and 33 kV then there is no problem. You can go ahead with it, just be careful not to accidentaly parallel them on the 15 kV side.

cheers

__________________
The time is ......now
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #4

Re: Parallel Operation of Transformers

11/22/2011 8:39 AM

That does make sense.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Mar 2011
Location: INDIA
Posts: 10
#2

Re: Parallel Operation of Transformers

11/21/2011 12:20 PM

If the primary is fed from the same single source and if impedance matches, then momentary paralleling shall be done.

Register to Reply Off Topic (Score 7)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Parallel Operation of Transformers

11/22/2011 5:55 AM

Intriguing Question! What is the vector group of the transformer? What are the loads connected to the 33kV Side and to each of the 15kV Side? Are they feeding semiconductor loads by any chance?

Register to Reply
Participant

Join Date: Sep 2011
Posts: 4
#6
In reply to #5

Re: Parallel Operation of Transformers

11/22/2011 6:36 AM

the transformers have the same vector group of Ynd11d11 and the connected loads with each of the lines vary from household lighting to cement factories.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#10
In reply to #6

Re: Parallel Operation of Transformers

11/23/2011 9:07 AM

If the loading on the unparalleled 15kV sides is unequal, then it could cause differential voltage drops in the two 15kV secondaries and thus would cause circulating currents between them. The transformer differential protection could spuriously trip.

Register to Reply
Active Contributor

Join Date: Dec 2009
Location: Malaysia
Posts: 14
#8

Re: Parallel Operation of Transformers

11/23/2011 12:34 AM

On my experiences previously, it was the same issued; where vector Tx is same, different input of Tx, and output need to be merge out together without disturbing the transmission line. Base on simulation programme we'd identified the output is fluctuated base on load demand, what we suggesting is the process behaviour (output) should auto synchronised with impedance generated with load demand.

__________________
LifeCycle of Engineering
Register to Reply Score 1 for Off Topic
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#9

Re: Parallel Operation of Transformers

11/23/2011 7:41 AM

What's the worst thing that could happen?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Anonymous Poster #1
#11
In reply to #9

Re: Parallel Operation of Transformers

12/11/2011 12:37 PM

poof ,boom!