Phase Reversal Provision in MPB

11/22/2011 11:55 PM

Dear all,

We installed a 2500 Amps Main Panel board with Phase Reversal ACB. We configure

"R Y B and Y R B" through 2500 Amps ACB on commercial Power. The Phase sequence will change automatically if there is a change on commercial power side. but it does not work if reversal done on "YBR, BYR,BRY,RBY.

It is cost effective if we provide 4 more ACB's to avoid such problems. I will highly appreciate if some body give me agood soloution to combat with the problem.

hanks and bestv regards.

Khawaja Raisuddin

__________________
Khawaja Raisuddin, Manager Project Technical
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: PHASE REVERSAL PROVISION IN MPB

11/23/2011 12:54 AM

This sounds really, really weird. There should be no reason for the grid ("commercial side") to have inconsistent phase rotation. You should be able to test your own network, just once, with a phase protection relay or other instrument. If the rotations match, fine; if not, simply interchange two phases on your side.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: PHASE REVERSAL PROVISION IN MPB

11/23/2011 6:28 AM

It's down right bizarre, are you seriously saying the utility power reverses?

Sorry but I don't believe you.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Commentator

Join Date: May 2011
Posts: 84
Good Answers: 1
#3
In reply to #2

Re: PHASE REVERSAL PROVISION IN MPB

11/23/2011 3:57 PM

in pakistan .. may be..

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4
In reply to #3

Re: PHASE REVERSAL PROVISION IN MPB

11/23/2011 4:37 PM

I'd love to see a reversing turbine or diesel gen set.

Who knows? Anything is possible! (In your imagination).

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5
In reply to #2

Re: PHASE REVERSAL PROVISION IN MPB

11/23/2011 6:21 PM

Lines go down, linesmen too rushed and/or too stupid to know how to reconnect them in the proper sequence.

Heck, I had that happen once in Washington State! Took out an entire sawmill (who also was too cheap to have Phase Reversal protection on critical equipment).

What I don't understand is how this is being corrected with ACBs, and why it makes a difference if it is YBR or BRY or RYB, they are all the same relative rotation, should not be an issue.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Active Contributor

Join Date: Dec 2009
Location: Karachi, Pakistan
Posts: 22
#6
In reply to #5

Re: PHASE REVERSAL PROVISION IN MPB

11/24/2011 12:25 AM

Yes it happens and happens many time it is the mistakes of line man/Cable Jointer cost us a huge amount and 30 hours power generation, Change the sequence many times but doesnt come to the "RYB" position. Finaly after 30 hours we acheived our target. We already have sequnce "RYB and YRB" with 2 seperate ACB's and we found it is very much difficult to cover all the sequence through ACB's. Yes it is Pakistan and acommon error is there.

__________________
Khawaja Raisuddin, Manager Project Technical
Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#8
In reply to #6

Re: PHASE REVERSAL PROVISION IN MPB

11/24/2011 3:59 AM

It is a mandatory practice before carrying out any cable jointing/ overhead line conductor jointing work to test existing phase sequence of the system and repair works done accordingly complying with existing phase sequence.. In any case, if shifting of conductor(s) is not possible due conductor length, space constraints at the place of joint, cross conductor connection may be done but again,proper phase sequence must be checked and line connections should altered accordingly at the other end to have same phase sequence( source end and load end ). If the cable jointer does understand the method of checking of phase sequence and its importance in electrical power system, qualified supervisor must be present at time of work.

Manindra

__________________
Manindra
Register to Reply
Commentator

Join Date: Jun 2011
Posts: 67
Good Answers: 2
#9
In reply to #6

Re: PHASE REVERSAL PROVISION IN MPB

11/25/2011 7:22 AM

Best is to have a phase sequence relay which will trip your incoming breaker instantaneously if there is phase reversal. You can then change it manually by reconnecting the incoming cable phases in the correct sequence. You will only have to ensure sufficint length of final tails to enable this exercise. This is a rare occurence and I have not seen this happen in my 48 years of experience in India and Middleeast.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#10
In reply to #6

Re: PHASE REVERSAL PROVISION IN MPB

11/26/2011 8:23 PM

All I can say is the cable must be rubbish if you have to have it repaired frequently. Overhead lines would be glaringly obvious if there are crossed phases.

Any cable jointing I've been involved in, phase orientation has been of paramount importance. I can't believe that a cable jointer wouldn't understand this.

Maybe I've been lucky with jointers.

I trained up to do jointing so that I understood it, in those days it was an art form. No hot or cold shrink, but oil impregnated tapes and plumbing metal.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7
In reply to #5

Re: PHASE REVERSAL PROVISION IN MPB

11/24/2011 12:39 AM

What did it do? Unsaw some logs and put them back together?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

JRaef (1); Khawaja Raisuddin (1); Learner42 (1); manindra (1); muditmah (1); TonyS (3); Tornado (2)