100Kva Gen Set Failure

11/23/2011 7:04 AM

Hi Could somebody assist me to get solution to this my 100Kva perkins engine,When started working it works well but when loaded for a while the turbo charger becomes red.what might have gone wrong Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: 100Kva gen set failure

11/23/2011 7:07 AM

It sounds as though the engine is working harder as the load comes up. That would increase the amount of work the turbocharger is doing. Why should anything be wrong with that?

Has it always done this?

What does the genset manufacturer's technical helpline say on the topic?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Jul 2009
Posts: 8
#2
In reply to #1

Re: 100Kva gen set failure

11/23/2011 7:33 AM

Thanx PWslack,It has not been doing like this before just started three days ago and the manufacturer was silent about the troubleshooting in the manual.THE TURBOCHARGER BECAME RED LIKE FIRE,WHEN LOAD REDUCED 30-40% THE REDNESS DISAPEAR

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: 100Kva gen set failure

11/23/2011 7:38 AM

Please turn off Caps Lock.

What happens when the manufacturer receives a telephone call on the topic?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#4
In reply to #2

Re: 100Kva gen set failure

11/23/2011 8:31 AM

Have you been following your maintenance schedule?

The troubleshooting list for overheating is pretty straight forward.

Coolant?

Oil?

Maybe some help here.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Member

Join Date: Jul 2009
Posts: 8
#5
In reply to #4

Re: 100Kva gen set failure

11/23/2011 8:42 AM

The schedule has always been carried out according to specification,Could it be nozzle problem?the line to manufacturer is not through since the problem started

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: 100Kva gen set failure

11/23/2011 9:00 AM

Why is it perceived to be a problem? Isn't the turbocharger supposed to do some work?

Is the manufacturer on-board with this perceived problem? If not, why not?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#8
In reply to #6

Re: 100Kva gen set failure

11/23/2011 9:09 AM

Red hot seems like it may be running a little too warm.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #8

Re: 100Kva gen set failure

11/23/2011 9:14 AM

Without the original poster discussing it with the manufacturer and reporting here, one might never know for certain.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#7
In reply to #5

Re: 100Kva gen set failure

11/23/2011 9:05 AM

It could be lots of things. Check the coolant medium/flow to the turbocharger itself.

Is the turbocharger a Honeywell? Try checking with them directly. Or try to find the nameplate on the turbocharger, and contact whoever the manufacturer is.

It sounds like you've been abandoned by the people that sold you the unit.

Your problem is probably similar to this. If you continue to run it hot, you will ruin it..........................if it isn't already too late.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Active Contributor

Join Date: Dec 2009
Location: Malaysia
Posts: 14
#36
In reply to #5

Re: 100Kva gen set failure

12/02/2011 3:58 AM

If maintenance schedule is there, generator room ventilation is good and air filter doesn't choke, try to check;

  1. turbocharger exhaust coupling inlet, any choked or blockage?
  2. check the valve lash.
  3. check individual cylinder exhaust temperature?
  4. If exhaust temperature on individual cylinder in great different, check the injectors.

And also do load test on site 50%, 70% and 100%, take reading of;

  1. Engine power?
  2. fuel rate (LPH)?
  3. intake MFLD temperature?
  4. intake manifold kPa?
  5. intake air-flow m3/min?
  6. exhaust stack temperature?
  7. exhaust gas flow m3/min?

Then made comparison base on to standard operation manual or manufacturer performance data.
Note: if your generator is using advance ECU controller, all data said can be captured, however if your generator set using conventional starter and old version its is advisable to take amp, load, kW, fuel rate and temperature.

__________________
LifeCycle of Engineering
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10

Re: 100Kva Gen Set Failure

11/23/2011 9:15 AM

<...the line to manufacturer is not through since the problem started...>

Is there a problem with the telephone service in that location? What is it?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#11
In reply to #10

Re: 100Kva Gen Set Failure

11/23/2011 9:20 AM

I wonder where it came from?

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #11

Re: 100Kva Gen Set Failure

11/23/2011 9:22 AM

Well, that's one possibility.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Off Topic (Score 5)
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#13

Re: 100Kva Gen Set Failure

11/23/2011 10:05 AM

deletolaide,

Maybe nothing has gone wrong.

Have you been viewing the turbocharger under medium to bright ambient light and are now for some reason viewing the turbocharge in dim or no ambient light?

Under load a turbo will glow red.

The turbo after all is handling 1100F to 1200F exhaust gas right out of the cylinders.

Just a thought.

Regards - KJK

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#14
In reply to #13

Re: 100Kva Gen Set Failure

11/23/2011 10:27 AM

Good thinking.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #13

Re: 100Kva Gen Set Failure

11/23/2011 10:45 AM

Exactly. The manufacturer will know whether this is normal or not.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#16
In reply to #15

Re: 100Kva Gen Set Failure

11/23/2011 1:43 PM

The manufacturer. Eureka! Contact the manufacturer.

Someone should have suggested that before.

Do you suppose he ever will?

__________________
Semper Ubi Sub Ubi
Register to Reply Off Topic (Score 5)
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#17
In reply to #16

Re: 100Kva Gen Set Failure

11/23/2011 1:46 PM

I think they're out to lunch.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#18
In reply to #16

Re: 100Kva Gen Set Failure

11/23/2011 2:57 PM

EXCELLENT animation

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply Off Topic (Score 5)
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#19
In reply to #18

Re: 100Kva Gen Set Failure

11/23/2011 3:09 PM

Agreed: that is pretty funny. Sort of gory, but sometimes gory works.

PWSlack asked a variant of the same question six times... the .gif seemed applicable here.

Perhaps our OP can answer the very pertinent question.

__________________
Semper Ubi Sub Ubi
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jul 2008
Location: Anywhere I may be at the time
Posts: 661
Good Answers: 16
#20

Re: 100Kva Gen Set Failure

11/23/2011 4:36 PM

Perkins four stroke, basic, basic first.

Replace your air filter, even if it has been done recently. This is the first place to look when you have an overheating turbo.

Tim

Register to Reply
Power-User

Join Date: Jan 2010
Location: Atchison Village
Posts: 383
Good Answers: 39
#21

Re: 100Kva Gen Set Failure

11/24/2011 2:21 AM

Exhaust restriction AFTER turbo. Stiff bearings slowing turbo, due to cheap old oil Turbos are the worst for oil Buy the BEST available. Do you NEED the turbocharger? It just increases horsepower by stuffing more air into the cylinders.

__________________
Align culture with nature...
Register to Reply
Commentator

Join Date: Nov 2011
Posts: 56
Good Answers: 1
#22

Re: 100Kva Gen Set Failure

11/24/2011 5:53 AM

It is over heating most likely but what ? the turbocharger or the exhaust ? For a start I would suggest trying to locate the source of o/heating. If its the engine it could be a ignition timing problem probably from a slightly worn out cam .

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#23

Re: 100Kva Gen Set Failure

11/24/2011 8:15 AM

Red hot turbo charger is not that strange for prolonged high output operation.

We don't know whether this is now happening under the same loads where it never happened before or if the load has increased and it is now only working as hard as it was intended. Diagnosing sight unseen has its limitations.

As for contacting the manufacturer.... the OP said it was Perkins. Nuff said. Forget about any help from that lot.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Jun 2009
Location: Ontario Canada
Posts: 930
Good Answers: 31
#24

Re: 100Kva Gen Set Failure

11/24/2011 8:49 AM

Check to see if the exhaust system is restricted after the turbo. If the turbo is red hot the engine valves are also getting too hot. If there is an advance function on the fuel system maybe it is in the retard position that will heat exhaust components considerably. The plugged exhaust I have seen a lot although not on Perkins but Deutz it is quite common on older engines. Check the engine timing if exhaust is clear.

__________________
The fine line between cuddling and holding one down to prevent escape must be learned
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#25

Re: 100Kva Gen Set Failure

11/24/2011 9:41 AM

Is it a new set or was working earlier perfectly?. How much load(full or less) you are applying?. Are you applying the total load in single step?. Is the load equal to continuous or prime or standby rating?. If standby rating you should not apply full load suddenly.

__________________
pnaban
Register to Reply
Active Contributor

Join Date: Jul 2011
Location: Bangalore state Karnataka country india
Posts: 11
#26

Re: 100Kva Gen Set Failure

11/24/2011 10:58 AM

problem related to red hot turbo charger problem

01) check the air system impeller side out let for any leakage if air is leaking it turn to red hot turbo charger

02) check turbo condition

03) check aftercoolar for choke

04) check tappet setting

problem is truly related to air system.

if air is not sufficient more fuel is injected to cylinder maintain rpm which cause black smoke and red hot turbo charger.

__________________
nitin
Register to Reply
2
Guru

Join Date: Jul 2008
Location: Anywhere I may be at the time
Posts: 661
Good Answers: 16
#27
In reply to #26

Re: 100Kva Gen Set Failure

11/24/2011 11:16 AM

This is exactly why I had asked about the air filter (simple and stupid stuff first)...

I have seen this many, many times especially with Cat's. In one case the mechanic was reluctant to believe me, but later found that his crew had just been spraying paint in the engine room and plugged the filters.

There are many reasons why your turbo will become overheated nitin revankar gave you some good advise, take it and use it before going into the more complicated replys to this thread. Most replies are very true, but first check the basic more common problems.

Good Luck

Tim

Register to Reply Good Answer (Score 2)
Power-User

Join Date: Aug 2010
Posts: 209
Good Answers: 8
#28

Re: 100Kva Gen Set Failure

11/25/2011 7:16 PM

I know of one installation performed with OEM engineers where the turbo was red when the engine was performing exactly as designed. The complaint from the buyer. was solved by a cover over the turbo so the red would not be visible, since the turbo was running exactly as designed. Problem solved. (It was considerably larger than 100kva.) What exactly was the "failure"?

Register to Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#29

Re: 100Kva Gen Set Failure

11/25/2011 10:11 PM

have u serviced the generator and changed the fuel and oil filters? Check your turbo charger if the blades of fan bearings are free or stiff or not moving.Check your air filters and change or replace with good ones if they are choked or worn out as they may not be able to take in and filter enough air.Also ensure that your gen is not overloaded beyond its rated power.

Patrick whowha

__________________
Patrick Whowha
Register to Reply
Power-User

Join Date: Aug 2010
Posts: 209
Good Answers: 8
#30

Re: 100Kva Gen Set Failure

11/26/2011 7:03 AM

What is the actual performance data? Is the fuel consumption within specified limits? Are there unusual noises and/or vibrations connected with this "problem"? Are there other parts of of the system showing signs of overheating? Is the power output stable under constant load and responsive to varying load? Is the "redness" of the turbocharger the only sign of improper functioning?

So far there is no description of the problem.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#31
In reply to #30

Re: 100Kva Gen Set Failure

11/26/2011 9:43 AM

Also check whether the current,pf,voltage,power and frequency are within nameplate limits as well as constant or varying widely.

__________________
pnaban
Register to Reply
Active Contributor

Join Date: Jul 2011
Location: Bangalore state Karnataka country india
Posts: 11
#32

Re: 100Kva Gen Set Failure

11/26/2011 11:03 AM

hi Is there proper ventilation for the generator. what is ambient temperature and temperature near air filter. check for fresh air entry and hot air outlet from radiator. if hot air is recirculating rectify it.

__________________
nitin
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#33

Re: 100Kva Gen Set Failure

11/27/2011 12:04 AM

OP has not told us what the load is or was? Has he even checked?

I wonder if he has replaced the air filter yet as rationally suggested by others.

However, I still think it's OK. My experience with choked air filters involved flames coming out of the exhaust. A little rich? Filter was choked with Bogong Moths. All good once sorted and that turbo charger (on a CAT 1MVA) always glowed at night.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Active Contributor

Join Date: Dec 2009
Location: Malaysia
Posts: 14
#34

Re: 100Kva Gen Set Failure

11/29/2011 12:19 AM

I faced this kind of situation, address to one of the island that diesel generator meant as prime power to island.

After several inspections & measurements been made we founded; that diesel generator is under performance due to lack of routine an unplanned maintenance, parts of the problem contributors is air filter, diesel and air injection ratio, turbo charger bearing and contain of diesel.

What i can highlighted over here, routine and plan preventive maintenance is very critical in order to get best performance when applying load to engine.

Herewith some example of basic routine maintenance.

__________________
LifeCycle of Engineering
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jan 2011
Location: Jakarta
Posts: 162
#35

Re: 100Kva Gen Set Failure

12/01/2011 7:32 PM

In mechanically called Glowing Turbo, the cause may a lot but some :

1. Too much back pressure from your exhaust

2. Less air intake

3. High ambient temperature around the set

__________________
One system
Register to Reply
Register to Reply 36 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

deletolaide@yahoo.com (2); Doorman (2); khairul.asra (2); KJK/USA (2); kramarat (6); loadshare (1); nitin revankar (2); ormondotvos (1); Patrick Whowha (1); pillay (1); pnaban (2); PWSlack (7); roy hammy (1); Tim in Mexico (2); Wal (2); woodpower (2)

Previous in Forum: Top Connection 11.50-4 ACME Box   Next in Forum: Material For Spring

Advertisement