OH Line Transformer Earthing

11/24/2011 12:30 AM

Now I may be wrong on this but am I right in thinking that the earthing for a pole mounted transformer should be separate from the LV neutral / earth bonding?

My thinking is if there is a MV earth fault in the transformer where the neutral is earthed via the same rod, due to the voltage gradient in the ground the MV fault could be exported to the LV network.

My reason for asking is a friend has just had a new supply to his cottage, the electricity board has provided a supply with a separate neutral / earth. The earth being provided by the same rod as the MV transformer earth.

I don't think it is safe

Sorry about the childish drawing but it shows what I mean

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster #1
#1

Re: OH line transformer earthing

11/24/2011 1:59 AM

I really don't think it would matter if the grounding system had been chosen properly. Afterall the maximum voltage permitted at the system ground is of the order of few volts under the designed fault condition.

There is a good step by step procedure here, it too doesn't show a separate earth connection.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: OH Line Transformer Earthing

11/24/2011 3:10 AM

http://en.wikipedia.org/wiki/Earthing_systems

A is TT

B is TN-CS

No problem.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#3

Re: OH Line Transformer Earthing

11/24/2011 7:44 AM

Hi Tony,

For what its worth, this is how my own service was set up in 1997.

The utility pole out by the road has a 4160/240/120V - 15KVA transformer mounted on it. NOTE: Where I live, every house (service drop) has a pole mounted transformer.

There is a bare copper conductor running down the pole from the ground lug on the transformer and the lightning arrestor to a driven ground rod at the base of the pole.

There is a second pole on my property that conveys the secondary conductors to my meter. At the meter there is a bare ground conductor from the meter cabinet to a driven ground rod at the base of this 2nd pole.

From the second pole the secondary conductors go underground via rigid steel conduit to my home service panel.

My 200A service panel has a ground conductor from the panel to the steel water pipe coming in from the well.

I agree with you regarding the need for separate (multi path)bonding. My concern is the lack of redundant bond points.

Just my 2 cents.

Great illustration by the way

Regards - KJK

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#4

Re: OH Line Transformer Earthing

11/24/2011 9:43 AM

In North America, at least, it has become the defacto utility standard to use a common neutral, pole ground system for both the primary and secondary distribution systems.

Why...

1) Cuts down on an additional neutral conductor.

2) Improves the realiability of their coordination systems.

One of the more esoteric benefits is that... redundent return paths, through the "single neutral" system allows for additional paths back to a source.

How does this help... if house A were to loose its neutral connection because of a failure in the consumer service drop, the chance that a ground return back to the source through a lower impedance path found in a neighbours ground electrode and then back to the common utility neutral then to the transformer, much improves the ability of the utility system to maintain the voltage levels delivered to the effected house at close to design levels.

This wont flow any, or very little, imballance current back to the source. The benefit comes from helping to ensure voltage levels stay normal or as close to normal as possible in event of a dropped neutral. Otherweise... 120v devices get connected in series across a 240v source.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Active Contributor

Join Date: Oct 2009
Posts: 24
#5

Re: OH Line Transformer Earthing

11/26/2011 1:12 AM

Under fault conditions your fuses and mcb should isolate due to over currents.

So your earthing must be common from source to consumer point

My thinking SIR.

JS