What is the short circuit setting of MCCB

__________________
lets talk some technical
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Short Circuit Setting of DC MCCB

11/26/2011 10:58 AM
Register to Reply
Active Contributor

Join Date: Jun 2011
Location: Gurgaon, Haryana, India
Posts: 10
#3
In reply to #1

Re: Short Circuit Setting of DC MCCB

11/28/2011 12:07 AM

Are the setting of AC & DC MCCB's are same?

__________________
lets talk some technical
Register to Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#2

Re: Short Circuit Setting of DC MCCB

11/27/2011 5:26 PM

Your setting of the the mccb depends on the load current and the factor k which is dependent on the cable sizing of your installation. Short circuit current = rated load current multiplied by the factor k.When you know the size of cable used for the installation,check your table for the right k value.We have 1.0,1.5,1.8,2.5,3.5 etc based on the size of cable in the installation.

set or adjust the mccb short circuit current to the calculated value to trip your load or installation from the damaging effect of short circuit fault.If the mccb has no selectable ranges,the buy one with the exact value in the market to protect your load.

Read further on short cct calculations for protective devices like breakers and fuses.