Alternator

11/26/2011 8:08 AM

Why are power capacitors are turned off when supplying power from generator?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Alternator

11/26/2011 10:45 AM

So they will be lighter?

Register to Reply Score 1 for Off Topic
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Alternator

11/26/2011 11:23 AM

Because that's what the engineer says to do.

Since you have not explained where these capacitors are in your power distribution circuitry or what type of power generator you have, this is the best answer you will get.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Alternator

11/27/2011 2:07 AM

These may be power factor correction capacitors. When running on the genset, there is no billing penalty for low power factor, so the capacitors may not be needed. In some cases, they may still be helpful; I don't know if there are disadvantages.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: Nov 2011
Posts: 1
#4

Re: Alternator

11/27/2011 2:12 AM

You will get answer from following link. This blog is in Spanish language but you can translate in English. I hope you will get exact answer of your question.

(Link removed)

Register to Reply
Anonymous Poster #1
#5

Re: Alternator

11/27/2011 2:14 AM

Also there is another erason, current transients at switch on, with all the capaicitors on line, which in your case might damage your generator.

Register to Reply
Member

Join Date: Aug 2010
Posts: 9
Good Answers: 1
#6

Re: Alternator

11/28/2011 1:44 AM

I'm not sure about the very latest excitation systems for gen-sets but some of the ones that I have encountered do not handle leading currents very well or indeed regeneration. It seems that although there is forcing to increase the alternator field quickly the field is normally fed via diodes and so the decay of the field flux and thus the excitation voltage is much slower going down. That plus some of the control systems are not phase sensitive in their measurement of current means the system is likely to go unstable if only capacitive current is seen by the generator. Thus the general rule disconnect cap banks if using a gen-set.

Register to Reply
Active Contributor

Join Date: Jun 2010
Posts: 15
#7

Re: Alternator

11/30/2011 11:31 AM

Consider a case in which load on Genset is disconnected while Capacitor bank remains connected. Now in such a condition, the voltage at alternator terminals will rise and it may damage AVR. Also, Tornado has rightly pointed out there is no pf penalty on Genset. Hence it is always advisable not to connect Capacitor Bank on genset.

Register to Reply