Why are power capacitors are turned off when supplying power from generator?
Re: Alternator
11/26/2011 10:45 AM
So they will be lighter?
Re: Alternator
11/26/2011 11:23 AM
Because that's what the engineer says to do.
Since you have not explained where these capacitors are in your power distribution circuitry or what type of power generator you have, this is the best answer you will get.
Re: Alternator
11/27/2011 2:07 AM
These may be power factor correction capacitors. When running on the genset, there is no billing penalty for low power factor, so the capacitors may not be needed. In some cases, they may still be helpful; I don't know if there are disadvantages.
Re: Alternator
11/27/2011 2:12 AM
You will get answer from following link. This blog is in Spanish language but you can translate in English. I hope you will get exact answer of your question.
(Link removed)
Re: Alternator
11/27/2011 2:14 AM
Also there is another erason, current transients at switch on, with all the capaicitors on line, which in your case might damage your generator.
Re: Alternator
11/28/2011 1:44 AM
I'm not sure about the very latest excitation systems for gen-sets but some of the ones that I have encountered do not handle leading currents very well or indeed regeneration. It seems that although there is forcing to increase the alternator field quickly the field is normally fed via diodes and so the decay of the field flux and thus the excitation voltage is much slower going down. That plus some of the control systems are not phase sensitive in their measurement of current means the system is likely to go unstable if only capacitive current is seen by the generator. Thus the general rule disconnect cap banks if using a gen-set.
Re: Alternator
11/30/2011 11:31 AM
Consider a case in which load on Genset is disconnected while Capacitor bank remains connected. Now in such a condition, the voltage at alternator terminals will rise and it may damage AVR. Also, Tornado has rightly pointed out there is no pf penalty on Genset. Hence it is always advisable not to connect Capacitor Bank on genset.