I want to the connection between an overload relay & 3 phase induction motor.

If the induction motor draws a FLA of 123A, what should be the rating of the overload relay?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Overload relay

11/28/2011 5:26 AM

The correct overload relay will embrace the full load current of the motor within its range of available settings.

  • If it's larger, it might not trip before the motor burns out, so it will not fulfil its intended purpose.
  • If it's smaller, the motor will trip the overload before full load current is reached, which can be classed as "nuisance tripping".
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: Overload relay

11/28/2011 5:55 AM

PWSlack's answer is comprehensive.

To probe a bit, at this power level, are you using DOL starting? Unusual, i may say. If you are using a ΥΔ starter for example, it is normal for the relay to be within the Δ, and you should set it to the phase current, ie., 123/√3 A.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: Overload relay

11/28/2011 11:34 AM

"If you are using a ΥΔ starter for example, it is normal for the relay to be within the Δ, and you should set it to the phase current, ie., 123/√3 A."

Oooohh, I'll bet that confused him...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#4
In reply to #3

Re: Overload relay

11/28/2011 8:41 PM

That was the general idea

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#5

Re: Overload Relay

11/28/2011 11:13 PM

If you are in NEC (or CEC) world, the overload setting of the DOL starter motor is generally no more than 1.15% of the motor nameplate full load current.

Here is the maximum overload setting for continuous duty motors from NEC 430.32 (A)(1):

Motors with a marked service factor 1.15 or greater: 125% of nameplate full load current

Motors with a marked temperature rise 40°C or less: 125% nameplate full load current

All other motors: 115% nameplate full load current

I think PWSlack's comment is per IEC standard.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: Overload Relay

11/29/2011 3:16 AM

1.15%? Really?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#7
In reply to #6

Re: Overload Relay

11/29/2011 8:08 PM

Thanks for pointing it out. I think, it is understood that 1.15% is a typo. It should be 115%.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)