PLC Fuse

12/03/2011 12:11 AM

If the PLC is of 24Vdc power; to which i have to give 4A fuse; what type of fuse should i generally use?
Are fuses necessary at the PLC digital I/O's? Where 24V is given to PLC input is of 4mA and outputs are of 2A. If needed what type of fuses should i place there?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: plc fuse

12/03/2011 12:29 AM

It is about time you start searching on your own...

plc fuse

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Off Topic
Associate

Join Date: Oct 2011
Posts: 25
Good Answers: 1
#2

Re: PLC Fuse

12/03/2011 10:34 PM

The fuse goes inline on the 24 vdc supply to plc. I prefer to use small circuit breakers. Circuit breakers are really convenient when doing maintenance. Otherwise any 4 amp fuse rated for 24 vdc OR Greater voltage is fine. If the inputs are not supplied from the plc they should be fuse protected at their source (this would be an uncommon configuration).

Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#3

Re: PLC Fuse

12/03/2011 11:08 PM

it would be common to use fast acting fuses for circuit boards

time delay fuses for motors

different boards can be more or less tolerant to abuse

more protection is better than less

it gets real expensive when a motor shorts out & ruins the output board

there can be issues with compliance with regulations, that require protection devices

the best configuration, depends on many factors including

duty cycle, type of load & common configurations on other equipment in your facility

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#4

Re: PLC Fuse

12/04/2011 1:05 AM

Ok Sujinvipin you want to know why to use a fuse, depending on the application i would possibly use a seperate fuse for each I/O.

The reason that I would do this is for easy identification of where a problem circuit is, if the fuse is blown I is that input that is causing the problem, this can and will reduce trouble shooting time on time critical equipment.

Cheers

Joe

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: PLC Fuse

12/05/2011 3:39 AM

Doesn't it depend upon the size of the wiring? The wiring is, after all, what the fuse is there to protect!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
Canada - Member - New Member

Join Date: Feb 2010
Location: The Great White North
Posts: 185
Good Answers: 13
#6

Re: PLC Fuse

12/05/2011 12:52 PM

The fuse comming from your power supply should be capable of handling the output current of your power supply and not be too large a value for the wiring you are using. Generally a slow blow fuse is used here.

Ideally each input should be fused seperately with a 0.5 amp fuse. However in a practical world I might use 1 fuse for as many as 4 inputs. Make sure that each input can be disconnected easily for troubleshooting reasons. If an input shorts it can pull down the power suply to 0 Volts and if it's not fused correctly this can be hard to find.

Each and every connected output should be fused. 0.5 amps for 24v and 2 amps for 120v. This is to protect the output triacs or relay contacts from failure in a short circuit condition. These values are general values, your needs may differ.

You can do with less fusing, but it will cost you more in down time and repairs.

What you are protecting is the power suply from overload, and your output cards from excessive current. You don't want to have to replace a card because of a short circuit in an attached device.

Good luck Elroy

__________________
Knowledge makes what was impossible, seem easy.
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

AKdude (1); Elroy (1); Garthh (1); Joe Sparky (1); kvsridhar (1); PWSlack (1)