Load Schedule

12/05/2011 2:52 AM

In load schedule the power factor for 0.85 for motor loads >7.5kW, 1.0 for heater loads and 0.8 for all other loads. if thus all load is in the system , which power factor to choose.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Reg: Load schedule

12/05/2011 3:31 AM

Wouldn't that depend upon the vector sum of all the loads in the system?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Good Answer (Score 2)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Reg: Load schedule

12/05/2011 3:37 AM

To simplify conservatively, you could choose the most adverse case, namely 0.8. Otherwise, a weighted average will be somewhat more favorable. See previous.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3

Re: Load Schedule

12/05/2011 10:06 PM

Hints: From the power factor (p.f) and the KW of each load, find the KVAR of each load. Then find the sum of all the KWs and sum of all the KVARs. From total KW and KVAR, find the resultant power factor.

Note: This should be enough for some one who knows the relation between KW, KVAR, p.f and KVA.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Score 1 for Good Answer
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#4

Re: Load Schedule

12/06/2011 4:45 PM

The power factor to be maintained is the minimum value approved by the power supplier with out penalty which varies with the supplier. The most desirable value of Pf is unity as KVA will be equal to KW and KVAR will be zero. Most of the power load being inductive and result in low pf. To improve pf you have to add capactor in the circuit. To maintain the the pf value nearer to unity large capacitor units have to be added and that will not be constant . It is adviceable to use automatic pf correction unit (APFC panel) to be added to system with appropriate pf settings .

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5

Re: Load Schedule

12/06/2011 10:07 PM

PF of a mixed load depends upon the diversity and load factor and is time dependant. Best way is to install a logger/recorder and plot the graph and take the maximum,minimum and average or mean value depending on the purpose.

__________________
pnaban
Reply
Reply to Forum Thread 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

msamad (1); pnaban (1); PWSlack (1); Tornado (1); V.I.Abraham (1)

Previous in Forum: Induction Motor Starting   Next in Forum: Heat Load Calculation for Lighting System

Advertisement