If the d/p cell is not located at an elevation that corresponds to 0% level in the tank, it must be calibrated to account for the difference in elevation. This calibration adjustment is called zero elevation when the cell is located above the lower tap, and is called zero suppression or zero
Figure 7-5: Click on figure to enlarge.
depression when the cell is located below the lower tap. Most d/p cells are available with elevation and suppression ranges of 600% and 500% of calibrated span, respectively, as long as the calibrated span does not exceed 100% of the upper range limit of the cell.