Adjusting Vacuum Reading for Gauge Position

12/12/2011 10:47 AM

I am trying to determine the Total Head of a new water Pump and I want to compare the results with the manufacturer's specifications. How do I adjust readings for gauge position as the gauges are not at the center line of the pump??

The pump's inlet (suction) gauge is 8.0 inches above the pump center line and I get a reading of -6 inch Hg; this is a negative number so I might call it inlet pressure. If I change the sign of the reading to positive then I might call it "inches of mercury vacuum" (inHg), and the gauge would have a range down to a 30 inHg vacuum.

The Discharge pressure gauge is 14 inches above the pump center line and I get a reading of 35.5 psi on the gauge.

Normally, I would place the inlet and discharge gauges are the same elevation so that the elevation difference between the gauge position and and center line of the pump is not a factor in the calculation of total head, but in this case they are at different elevations.

What is the Total Head of the Pump?

More to the point of my Question title - How do I adjust the reading of each gauge to determine actual pressure?

For the Inlet (Suction) gauge, I would think that the gauge would read 8.0 inches of water pressure less than if the gauge were at center line of the pump. Does this mean I get a higher negative inch Hg reading or a higher positive inch Hg vacuum reading??

I am converting all the pressure and vacuum readings of various units to meters of water for the total head calculation.

So far I got -8"Hg = -0.2032 meters and the inlet reading of -6 "HG = -2.072 m H2O

I converted the discharge pressure of 35.5 psi to 24.963 m H2O

I think that the 14 inch from center line distance should make the discharge gauge read 14" x 0.0254 m/inch = .3556 m H20 less than actual.

So, to adjust gauge readings for elevation, I think that I need to convert the 8.0 inches to m H2O and add? or subtract? this negative suction number to/from? the negative reading number, which was also converted to m H2O; i.e. - 2.072 m H2O +/- -0.2032 m H2O = -1.868 or should I get -2.2752 mH20??

Similarly, On the pressure side, should I add or subtract 0.3556 m to/from the pressure reading of 24.963 m H20 ?? to get 25.318 m H20 or should I get 24.6074 ??

And then is my actual Total Head then 27.19 m H20 or some other number??

Flow rate at these readings is 11.9 L/s and gauges are located close to inlet and outlet.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Adjusting Vacuum Reading for Gauge Position

12/12/2011 11:04 AM
  • There is no practical reason to go below 10mm of water gauge precision.
  • A pressure gauge is only accurate to a few percent.

How do these concepts affect the sensitivity of the calculations above? Do they remove the need for the calculations?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: May 2011
Posts: 27
Good Answers: 3
#7
In reply to #1

Re: Adjusting Vacuum Reading for Gauge Position

12/13/2011 8:00 PM

Thank you for your comment on precision.

As a general rule, I round off the numbers to the required precision after the calculations are done because I have found that if I round off the numbers first, before doing a calculation, then the result can, on occasion, be different than if I had used the actual number in the calculation and is only the same if I reduce the precision, sometimes to less precision than required. Well, OK, but then what is the required precision?

The pump manufacturer supplied performance specifications with a precision of +/- 0.05 meters H2O; i.e. the TDH at the duty point is 21.4mH2O so I interpret this to mean observed performance should be between 21.35 and 21.45mH2O

This would be about 0.05/21.4*100 = 1/4%

Yes, then, accuracy of the reading from a general use gauge, with a precision of say, 2%, will be less than this specified precision.

With regard to the effect of the gauge not being at the center line of the pump; however, the physical distance can be measured fairly precisely. In this case, the 8 inches would be 8" +/- 0.25 inches so the pressure due to 8"H2O would be 0.2032 meters +/- 0.0064 meters. This precision is more precise than the 0.05 meter manufacturer's specification precision.

[I just noted that in the original question I mistakenly said "So far I got -8"Hg = -0.2032 meters...." What I was referring to was than the gauge that read in "Hg was 8" above the centerline so I thought I would need to subtract 8" of water pressure, i.e. add a negative number -8"H2O = -0.2032mH2O pressure to the gauge reading.]

So to review.

The effect of having the inlet gauge 8" higher than the center line of the pump will change the reading of the inlet (suction) gauge by 8"H2O or 0.2mH2O [ I still need to learn if this will increase or decrease the measured value by 0.2mH2O ]

The measurement that I got from the inlet gauge was -6"Hg = -2.072mH2O

Hmm. It looks like the position of the gauge has no significant impact on the Inlet Head measurement. i.e. If I measure the inlet (suction) pressure to be -2.072 m H2O and I round this to -2.1m then adding or subtracting .0064 meters from this, would not change or adjust the reading of -2.1m

Since Total Head is what I am trying to measure, then the vertical distance between the inlet and discharge gauges is perhaps more important than the distance from pump center line to a particular gauge. Here 14" - 8" = 6" or 0.1524 mH2O

Again, perhaps I can conclude that if the inlet and discharge gauges are less than 8" or 0.2m vertical distance apart then no adjustment is needed because the adjustment would not change the calculated Total Head. If gauges are say 60" or 1.5m vertical distance apart then an adjustment for gauge position would be warrented.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Adjusting Vacuum Reading for Gauge Position

12/12/2011 11:32 AM

Why would you expect pressure on the suction side of a pump?

Elevation = head, it's that simple.

As PWS says, I think you are after too much precision. I also wonder how much confusion you will introduce by changing the units everyone is used to working with now, to something new.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#3

Re: Adjusting Vacuum Reading for Gauge Position

12/12/2011 8:33 PM

If the gauge is above the pump you should subtract the water column (pressure) in the sensing lines from the absolute pressure indication. If the suction gauge had air in it when installed the air will expand as pressure decreases, thus displacing water in the sensing line and decreasing the head effect to the indication. Do not mistakenly presume that the gauge sensing lines are full of water.

Register to Reply
Anonymous Poster #1
#4

Re: Adjusting Vacuum Reading for Gauge Position

12/12/2011 11:28 PM

Pls try to Install a pressure gauge, say 10 mtrs above the existing Pressure gauge in discharge.. As per your THEORY, the upper gauge should show a higher pressure by about 14.7 psi.....(1atm= 14.7 psi = 10 mtrs of Water Head= 30 in of Hg)

I think this will not happen..Water is not static, its moving. Pls inform the feed back.

Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#5

Re: Adjusting Vacuum Reading for Gauge Position

12/13/2011 12:15 AM

The most effective way to "correctly" measure pump pressures (or any other multiple-source system) is to install ONE very high quality gauge on a header with ALL of the measuring points connected to the header with ball or plug valve isolation. Mount the header and gauge anywhere above ALL of the measurement points and be sure that all lines are "flooded".

Just open one valve at a time and record the reading on a simple chart. Include appropriate "blank" spaces on the chart to note various differences that will be used to compute performance.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Anonymous Poster #1
#6

Re: Adjusting Vacuum Reading for Gauge Position

12/13/2011 11:07 AM

We all have missed the point and the question it seems..

Inlet = -6 inches of Hg = -81.6 inches of Water

Outlet = 35.5 psi = 983.35 inches of water

Diff in Elevation of Suction and Discharge = 14 - 6 = 8 inches

Head developed by Pump = 983.35 - (-81.6)+8 = 1072.95 INCHES OF WATER = 38.6 PSI = 27.25 Meters of Water.

Hope it satisfies yr querries.

Pls verify the conversion factors before you conclude.

Register to Reply
2
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#8

Re: Adjusting Vacuum Reading for Gauge Position

12/13/2011 9:28 PM

How good is your pressure gauge?

Pressure gauge error can dwarf the hydrostatic head pressure error due to installation elevation.

General purpose pressure gauges are known as 3/2/3, ±2% uncertainty from 10 o'clock to 2 o'clock, ±3% on the remainer of the scale. Better quality gauges are 1% or 0.5%, if not abused, but the increase in cost means they're not always used in the field.

When you do a differential pressure measurement with two gauges, the error can be opposite (one high, one low) on each measurement, seriously increasing the total percentage error.

Suppose you are using a 1% 100 psi gauge on the discharge and a 1% compound -30"Hg to 60 psig gauge on the suction side.

The discharge side uncertainty is ±1psi.
The suction side uncertainty is ±0.9 psi.
If the high side gauge reads high by 1 psi and the low side reads low by 0.9 psi, then your DP is off by 1.9psi, an error of 5.4% at 35 psi. And the gauges are "in spec".

In comparison, the 8"w.c. (0.29 psi) hydrostatic elevation error is a mere 0.8% error at 35 psi.

Why aren't pump measurements like that taken with a true DP gauge, or better yet, an indicating DP transmitter at 0.2% uncertainty (yeah, power pack, weight, ya-da ya-da).

Register to Reply Good Answer (Score 2)
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#9
In reply to #8

Re: Adjusting Vacuum Reading for Gauge Position

12/13/2011 11:35 PM

Sweet!

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Ace Boeringa (1); Anonymous Poster (2); Dug (1); energygod (1); Iris (1); lyn (1); PWSlack (1); Wal (1)