Earth Resistance

12/14/2011 3:41 AM

We have made two earth pits for our DCS system and 4 earth pits for our power supply panels etc. All are in a row.Distance between each earth pit is 5 mtrs and the earth pits are 2 mtrs away from the building.When we checked Before connecting earth flats to the earth pits we observed continuity between all the earth pits. In that area the earth resistance was 0.15 ohms.If the earth resistance is low is it possible to get continuity between earth pits eventhough there is no physical connection between the pits(i.e.electrodes).Pl clarify.

T.Sriram

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: earth resistance

12/14/2011 4:36 AM

Of course. The measurement is revealing that fact.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Oct 2011
Posts: 9
#2

Re: earth resistance

12/14/2011 5:48 AM

Hi thiagarajan sriram./

Mr.PW's reply is enough ah?

Got it ah?

Register to Reply Off Topic (Score 6)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: earth resistance

12/14/2011 7:21 AM

Be happy, rather than complaining. Not many people would get an earth resistance of less than one Ohm, without inter-connecting the pits. You must be having a wonderful soil over there.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4
In reply to #3

Re: earth resistance

12/14/2011 8:50 AM

Maybe yes, maybe no. Resistance is a parameter between two locations. When measuring earthing resistance, it is very easy to accidentally measure cable resistance instead of the ground resistance. An earthing resistance of about 1/8 Ohms is possible but this is such an exceptionally low resistance claimed that it makes me wonder if this is real.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Associate

Join Date: Jun 2011
Location: ROUEN (in NORMANDY), 120 km from Paris, France, Europe, Earth, Sun Sytem, Milky Way, Universe.
Posts: 39
Good Answers: 3
#5

Re: Earth Resistance

12/15/2011 1:08 AM

Good morning,

Earthing resistance varies every times all through the year, depending on your climate. Your value of 0.15 ohms is accidentally good. Next time (i-e, within 6 monthes) it will be less good, etc. Except if your earthing pits are collected through a trench, correctly erected, full of a good sand, etc. and all your rods connected through a bus bar of, for instance, a bare copper of 100 sqmm. Except in that case, earthing continuity through the soil is, consequently, not guaranteed. You must, at first connect all your rods, make a new check of that value and then be able to evaluate the new connections. For memory, for electrical circuits, you need only one ohm of value, if your switchgear is in metal and your power cables of pvc.

Best wishes and merry christmas to everybody, BRZK.

__________________
That's all, Folks. Take some time to learn where you live...
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6
In reply to #5

Re: Earth Resistance

12/15/2011 6:20 AM

Agree with most of your points BRZK. Bonding is critical through a serviceable connection. You don't really mean sand do you?

Questions for the OP. Did you measure the resistance to earth of each "pit"? Describe the soil type if you can. Are there other interred earthing elements at this site?

Although the achieved resistance to earth is important so too is the dimensioning of the system. eg a couple of knitting needles and some fuse wire might also give low ohm readings but do not constitute a good earth. Please describe the "pits".

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#7

Re: Earth Resistance

12/16/2011 6:12 AM

Exceptionally low value.What type of soil is there.Like other posts state u need to check the resistance during peak summer when soil will be dry.It is better interconnect all earth pits as planned.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#8

Re: Earth Resistance

12/16/2011 8:06 PM

Soil resistivity, theoretically, should not change with the weather.

This paper explores some of the practicalities of the issue:

http://www.cder.dz/download/upec-7.pdf

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply