Electrical Panel Room Details

12/16/2011 4:50 AM

Hi All,

In Electrical Panel Room how much distance we are maintained for panel to panel and Panel to Wall. How much depth we consider for Cable trench.

We are folowing panel to panel min. 200mm or maximum 700mm, In trenches depth depends on no. of cable trays. But Some times client will ask to me,

For which reference you are consider for considering the depths and distances

Explain me briefly or Inform to me standards are there for clearances.

(ex. IS standards, IEC standards).

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Electrical Panel Room Details

12/16/2011 5:24 AM
  • Can the door open fully?
  • Can someone work there with the door open?
  • Is there sufficient light for the individual to work there safely?
  • Can other equipment go past the panel with it installed?
  • Can someone gain access to the cable trench to pull and install the cables?
  • Is the trench big enough to get the bending radii required on the cables?
  • Etc., etc.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 3)
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#2

Re: Electrical Panel Room Details

12/16/2011 5:53 AM

The question is too general .There are several factors to be considered .

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#3

Re: Electrical Panel Room Details

12/16/2011 7:09 AM

After considering all the points of GURU,

Minimum Safety Clearances as per IS / Factory Inspector

Rear Side of Panel - 1000 mm

Front Side of Panel - 1000 - 1500 mm

At least one side of Panel shall be 1000 mm away from wall , if panel is double front.

Other wise, no restriction - only 50 mm will also do.

Top roof of Panel Room - Min. 16' as per Factory Act

Depth of trenches - depend largely upon the maximum cable size

Generally, 1000 mm - 1200 mm would be suffice.

__________________
Exploring the Science of Electricity
Register to Reply
Anonymous Poster #1
#4
In reply to #3

Re: Electrical Panel Room Details

12/16/2011 7:35 AM

Thanks for the information this information is very usefull to me.

Is there any IS or IEC standard. Please inform to be and guide to me.

Thanks and regards,

Srinivas.

Register to Reply Off Topic (Score 5)
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#5

Re: Electrical Panel Room Details

12/16/2011 10:43 AM

Try this

Quite a bit of good information.

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6

Re: Electrical Panel Room Details

12/29/2011 6:56 AM

Pl. refer to the Indian Electricity Rules, 1956. One of the rules very clearly mentions the clearances to be maintained between panels & walls and between panels.

Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (1); harry potter (1); KJK/USA (1); nesubra (1); PWSlack (1)

Previous in Forum: Motor Bike Bulb Selection   Next in Forum: Motor Torque

Advertisement