Motor Torque

12/16/2011 5:27 AM

When we connect a Induction motor (6 terminal squirrel cage) to Delta and star position , whether it will deliver diffrent torque ? If YES , then how , because the stator excitation remains same in star or delta which will keep the field same.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#1

Re: MOTOR TORQUE

12/16/2011 5:50 AM

The torque will be 1/3 of rated torque as applied voltage becomes 58% of rated voltage.

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#3
In reply to #1

Re: MOTOR TORQUE

12/16/2011 7:18 AM

You Mean 2/3rd of the rated torque ?

__________________
Exploring the Science of Electricity
Reply Score 1 for Off Topic
Anonymous Poster #2
#4
In reply to #3

Re: MOTOR TORQUE

12/16/2011 7:22 AM

No since maximum power that can be delivered is 1/3rd.

Hence maximum load (torque) - assuming the minor change in rpm (slip) as negligible would be 1/3rd

Actual torque however as PWS said is depending on the load, and the power, rpm and thereby torque would be detrmined by the intersecting points of the OCCs.

Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#7
In reply to #3

Re: MOTOR TORQUE

12/16/2011 12:58 PM

He may have meant rated torque in star as a fraction of rated torque in delta. Starting torque in star is 2/3 (approx) of rated torque in delta.

__________________
Give masochists a fair crack of the whip
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: MOTOR TORQUE

12/16/2011 6:14 AM

It is the shaft mechanical load that determines the torque, not the motor.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#5

Re: Motor Torque

12/16/2011 7:50 AM

Do you mean the same voltage in each case, as in a star-delta starter? In that case, the full-load torque (and power) in star are about 1/3 of values in delta. Perhaps rather less, as according to data I have the current falls by more than the voltage, and torque varies as current2. So as voltage is down by 1/√3 = 0.577, current down by say 0.5, and torque by 0.52 = 0.25. As the starting torque in delta is about 2 x full-load torque, starting torque in star is about 2 x 0.25 = 0.5 x value in delta.

But if you mean the supply voltage is correct for the connection type (so √3 x higher in star) torque and power are the same for both.

__________________
Give masochists a fair crack of the whip
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: Motor Torque

12/16/2011 10:01 AM

Torque varies as the square of the voltage. In Star, the effective voltage across each coil in the motor is now phase to neutral, so it is lower by the square root if 3, which means 1/1.732 or 58%. Peak torque from the motor then is .58 * .58 = .33, or 1/3 of what it was when connected in Delta. Keep in mind however that IEC dual voltage motors are designed so that you connect in Star if you have the higher voltage, Delta if you have the lower; i.e. 380V = Star connection, 220V = Delta connection. I'm too lazy right now to look up a 6 lead motor diagram to see if that applies here and you didn't bother to post all of the necessary information anyway.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Score 1 for Good Answer
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#8
In reply to #6

Re: Motor Torque

12/16/2011 2:25 PM

380V star, 220V delta is no good if you want to use star-delta starting with the usual 380V supply. It has to be 380V delta (660V star).

The 6 terminals are connected the same whatever the voltages - for delta, bridge across in 3 pairs, and connect a supply phase to each pair. For star, bridge all 3 terminals in one row of 2, and connect supply to the other 3. Of course, for star-delta all terminals are connected separately, to 6 cable cores.

__________________
Give masochists a fair crack of the whip
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#9

Re: Motor Torque

12/29/2011 6:54 AM

Do you mean starting torque or full load rated torque?

Reply
Reply to Forum Thread 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Codemaster (3); electricalexpert65 (1); harry potter (1); JRaef (1); nesubra (1); PWSlack (1)

Previous in Forum: Electrical Panel Room Details   Next in Forum: Class-X CT for Differential

Advertisement