why some countries use 5th wire on thier low voltage overhead lines.
Pathfinder Tags: 5th wire system
Re: low voltage system
12/22/2011 1:14 AM
Sometimes four is just not enough?
12/22/2011 3:16 AM
Because TT earthing just sometimes isn't appropriate.
Engineering Fields - Electrical Engineering - Ron Nombri Engineering Fields - Energy Engineering - Ron Nombri Engineering Fields - Power Engineering - Eternal Power Papua New Guinea - Member - Ron Nombri
12/22/2011 4:44 AM
I've worked on 4 wire distribution systems, 5 wire system is interesting learning.
Kind regards, Ron
12/22/2011 10:11 AM
Earthing conductors aren't often used on overhead lines. The risk to persons as a result of a tree branch fracturing it and a fault occurring downstream of it are too substantial to contemplate.
The best opportunity to observe overhead earthing conductors, and hence 5-wire systems, are on long-distance medium- and high-voltage distribution networks. Low-voltage to domestic premises run overhead will usually go for TT, which doesn't involve running the earth conductor in the trees; the Earth itself is the earth conductor.
However, in distribution systems, there isn't much call for the neutral conductor, so in the 3n+1 wires seen, the odd conductor is simply a protective earth conductor. 3n+2 is a rare spot - take the I-Spy book!
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member
Location: Chennapattanam (Coromandel Coast of the Bay of Bengal).
12/22/2011 5:28 AM
Good Answers: 88
12/22/2011 7:46 AM
The fifth conductor (if you refere to the low side thin one) is used for street lighting and is live only at night. S.M.
Good Answers: 181
12/22/2011 11:22 AM
I should have remembered that. The street I lived on had them, but that's going back in to the mist of time.
Good Answers: 170
Re: Low Voltage System
12/29/2011 6:16 AM
It is called TN-S system and the 5th wire is the Protective Earth conductor.