Communication Signal Error

12/24/2011 3:53 AM

In a closed loop control system, where we have a HART Pressure transmitter communicating with a PLC using OMNI as HMI. The pressure transmitter is reading - 70psig in the field and on the OMNI in the control room is showing say 26psig. Please, what could cause this? I have checked the transmitter calibration OK. The continuity for the transmitter cables to the OMNI is 'continous', the fuses are OK too.

Can someone tell me please?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#1

Re: COMMUNICATION SIGNAL ERROR

12/24/2011 4:22 AM

You miss out what is probably the most important information.
Was the system working and has now failed? Or has it never worked correctly?
Set up a similar pressure transduce (A), on a short length of cable connecting to the PLC, all set up in the control room. This will give you a chance to play with communication settings and suchlike.
Check that you can get that all working ok. If that is ok, then take the pressure transducer (A) out to where the problem one is. Connect (A) to the cable run, if it is all still working fine then the cable is ok and the installed transmitter is faulty, if it's not ok there is a wiring problem.
Apply basic fault finding techniques slowly and methodically.
The alternative is to run around randomly changing things and panicking, a practice best left to trainees and managers.
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Aug 2009
Posts: 14
#3
In reply to #1

Re: COMMUNICATION SIGNAL ERROR

12/24/2011 5:15 AM

Thanks alot Del. Yes, the system had been working well and suddenly start showing this error when the former faulty HART 3051 Pressure transmitter (0-300psi) was replaced with a new one(0-10,000psi) and was re-ranged(0-800psi); After the installation, it was OK, but after awhile the fault surfaced. So, can a new transmitter display correct values on the LCD display and display different values on the OMNI?

Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#4
In reply to #3

Re: COMMUNICATION SIGNAL ERROR

12/24/2011 5:41 AM

So, can a new transmitter display correct values on the LCD display and display different values on the OMNI?
No idea I have no experience with that equipment, but if there is a length of cable and a communication protocol involved anything can happen!

Maybe a scope or serial data analyser is called for. It seems too much of a coincidence for more than one unit to fail in the same manner, so maybe the fault is in the wiring or at the receiving end... or good old finger trouble.
'Re-ranged' worries me... I'd leave everything exactly as it was, only change one thing at a time if possible.
Good luck
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Commentator
Venezuela - Member - New Member

Join Date: Aug 2010
Location: Venezuela
Posts: 88
Good Answers: 5
#6
In reply to #3

Re: COMMUNICATION SIGNAL ERROR

12/25/2011 8:33 AM

ThankGod,

Can you tell us the model (serial complete) for this pressure transmitter?

As mentioned above, it is very important to know what kind of output signal are you using, is it 4-20mA or Hart digital signal?

the new transmitter was re-ranged, but how about the OMNI counts in order to display the correct value?

Regards

JP

__________________
Instruments-guy-SAV
Register to Reply
Participant

Join Date: Dec 2011
Posts: 2
#8
In reply to #3

Re: COMMUNICATION SIGNAL ERROR

12/26/2011 12:10 AM

Just change the range of PT in OMNI from 0-300 to 0-800, this should solve your problem

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Aug 2009
Posts: 14
#9
In reply to #8

Re: COMMUNICATION SIGNAL ERROR

12/26/2011 5:25 AM

Thanks alot Srinivasanp, I had just done that; that was the problem. Am grateful.

I also want to thank all that contributed to this success.

Register to Reply
Power-User

Join Date: Sep 2011
Location: Near the New Madrid Fault. USA
Posts: 269
Good Answers: 1
#11
In reply to #3

Re: COMMUNICATION SIGNAL ERROR

12/27/2011 2:17 PM

Wow, that is a 10:1 turn-down ratio, may make the output real sensitive to "PV" changes.

__________________
It's not Rocket Science
Register to Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#12
In reply to #11

Re: COMMUNICATION SIGNAL ERROR

12/27/2011 3:00 PM

>"may make the output real sensitive to "PV" changes."

If the transmitter's output is used as a PV input to a PID loop, the PID loop's output will not be more sensitive (aggressive) with the scale change; on the contrary, a PID output would be more sluggish.

The original 4-20mA scale represented 0-300 psi, the re-ranged scale is 0-800 psi.

A 6 psi error on the 300psi scale is only 2% error.
A 6 psi error on the 800psi scale is only a 0.75% error.

For the same PID tuning constants, a 0.75% error will call for less output change than will a 2% error.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: COMMUNICATION SIGNAL ERROR

12/24/2011 4:25 AM

Pray to God to tell you the answer. If He actually does, then ThankGod.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#10
In reply to #2

Re: COMMUNICATION SIGNAL ERROR

12/26/2011 8:09 AM

Glad you found your problem.

---------------------------------------------------------------------------------------------------

God answers all prayers.

But sometimes the answer is NO.

In my experience, these have been the best answers.

"There are no atheists in foxholes." James Morrow

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Off Topic (Score 5)
3
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#5

Re: Communication Signal Error

12/24/2011 8:44 AM

Let's review:

transmitter reading: 70 psi
control room reading: 26psi

old max range: 300 psi:
new max range: 800 psi

error factor in ranges 800/300 = 2.66 = 266%
error factor in readings: 70/26 = 2.69 = 269%

Do you see a pattern?

What kind of signal does the transmitter output?
What does the signal represent?
How does the HMI interpret the signal ?

> can a new transmitter display correct values on the LCD display and display different values on the OMNI?

Ans: Yes, yours is doing exactly that.

Hint: You changed the transmitter's output range. So why would you expect the control room to interpret it correctly when the field device output was changed?

If the arithmetic is too complex, consider that
- it was working correctly
- you changed something out
- you get different readings after the change out
- the replacement is presumably working OK.

What changed?

Register to Reply Good Answer (Score 3)
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#7

Re: Communication Signal Error

12/25/2011 7:54 PM

You must recalibrate(re range) the receiver to the same scale as the transmitter.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

HiTekRedNek (2); Instruments-guy-SAV (1); Iris (2); Rockyscience (1); srinivasanp (1); ThankGod (2); Tornado (1); user-deleted-1105 (2)

Previous in Forum: Zelio Logic - Programmable relays   Next in Forum: Motorised Operated Valve

Advertisement