respected sir, Happy xmas to all secondary injection test of numerical relay with test kit(like omicron, maggar,etc) which test should be done and what is the fundamental of choosing phase angle between I1,I2,I3, and V1,V2,V3. How stability,pickup and other tests perform.please guide me or give some link to learn this. thanks

__________________
Curiosity made genius
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Secondary Injection Test of Numerical Protection Relay

12/25/2011 1:39 PM

There must be some reason for doing these tests. What is it?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#2

Re: Secondary Injection Test of Numerical Protection Relay

12/27/2011 5:55 AM

Questions should be specific:

Relay:

For balanced system:

I(R) + I(Y) + I(B) = 0 , Ø = 0 ; for no earth fault (E/F) condition

and

I(R) + I(Y) + I(B) ≠ 0 , Ø ≠ 0 ; i, flows for earth fault (E/F).

I(R) = I in R-Phase or I1 (as mentioned by the original poster above)

and so on.........

__________________
--
Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#3
In reply to #2

Re: Secondary Injection Test of Numerical Protection Relay

12/27/2011 6:24 AM

This is for Over Current Relays and not differential relays. There are two methods, one primary injection and the second secondary injection method for CT testing.

and so on...

__________________
--
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#4

Re: Secondary Injection Test of Numerical Protection Relay

12/27/2011 10:00 PM
__________________