Cable Rating for 250KW DC Motor

12/24/2011 12:03 PM

We are going to commission DC motor of 150 KW capacity & details are given below,

Drive Incoming:

Incoming supply 415 v ac

Drive outgoing:

Armature Voltage 415 V dc

Armature Current 330 Amps

Field Voltage 110 v dc

Field Current 7.3 Amps

Motor RPM:1000

Please give the proper calculation to find the Cable rating for DC Drive incoming cable & outgoing cable from Drive to motor(Both armature & field)

Thanx

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Cable rating for 250KW DC motor

12/24/2011 12:37 PM

There are many web sites that offer help for people who don't have a clue what they are doing.

I'd advise you to hire an engineer to supervise the commissioning of the motor.

But that's just what I'd do.

Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#2

Re: Cable Rating for 250KW DC Motor

12/25/2011 12:20 AM

Motor Magic 101 tutorial is in conference room 6

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Cable Rating for 250KW DC Motor

12/25/2011 3:56 AM

This task is not generally done by calculation. Instead, one looks things up in electrical code tables. In this case, the insulation class at or above 415v is 600v; then select conductors by amperage, accounting for ambient temperature and conductor configuration.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Cable Rating for 250KW DC Motor

12/25/2011 1:40 PM

Did Santa bring British Standard 7671?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

lyn (1); PWSlack (1); Tornado (1); Wal (1)

Previous in Forum: Testing Room Heater Coil   Next in Forum: Secondary Injection Test of Numerical Protection Relay

Advertisement