Leakage From Transformer Secondary Bushing

12/27/2011 11:01 PM

Sir,

After some repair work on my 250 kva 11/433 kva transformer their is a oil leakage from secondry LV bushing base side, my transformer is on load condition & i want to know can i run this for next 3 days without repair it, if no then what type of problems may occure.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Leakage from transformer secondry bushing

12/27/2011 11:19 PM

How fast is the leakage? What is the height of the LV bushing in question, in relation to the correct oil level in the transformer? Can you add oil to compensate for the leakage?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 3)
Associate

Join Date: Jul 2011
Posts: 32
#2
In reply to #1

Re: Leakage from transformer secondry bushing

12/28/2011 12:27 AM

sir,

Bushing level is 10'' lower to oil level, i mean bushing is in oil level

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: Leakage from transformer secondry bushing

12/28/2011 12:46 AM

Okay, how about the other two questions?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: Mar 2011
Posts: 2
#4

Re: Leakage From Transformer Secondary Bushing

12/29/2011 12:24 AM

Hi,mate,I'm working for a transformer bushing company named Trench, but we only produce HV bushings, dunno if I can help you wit your issues, pls send me some pic on site if that is possible.Cheers.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Leakage From Transformer Secondary Bushing

12/29/2011 4:45 AM

I wouldn't advise that. Oil level may go below the windings and might cause an insulation breakdown or even a fire.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #5

Re: Leakage From Transformer Secondary Bushing

12/29/2011 5:09 AM

I don't know to whom you are responding. The best solution is probably to power down the transformer and repair/replace the leaking bushing. But in the meantime, it is logical to keep the oil topped up, with frequent monitoring.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - Ron Nombri Engineering Fields - Energy Engineering - Ron Nombri Engineering Fields - Power Engineering - Eternal Power Papua New Guinea - Member - Ron Nombri

Join Date: May 2007
Location: Papua New Guinea
Posts: 174
Good Answers: 3
#7

Re: Leakage From Transformer Secondary Bushing

12/30/2011 10:12 PM

For low oil level in transformer/bushing, if you have a thermograph, do thermal image scans of the transformer radiators while it is in operation. The mages will show dim for region without oil and brighter image is the areas with oil.

Perform a temperature rise test on the transformer with an infrared camera. The surface temperature of the tank must not be more than 20°C higher than the top oil temperature of the transformer.

Infrared Temperature Criteria-NASA

Criticality Temperature Above Reference Condition
Nominal 0 to 10 °C Nominal possibility of permanent damage. Repair next maintenance period.
Intermediate 10 to 20 °C Possibility of permanent damage. Repair soon.
Serious 20 to 40 °C Probability of permanent damage to item and surrounding area. Repair immediately.
Critical Over 40 °C Failure imminent.

This may assist your decision on the level of maintenance on the transformer.

__________________
Kind regards, Ron
Register to Reply Score 1 for Good Answer
Associate

Join Date: May 2010
Posts: 46
Good Answers: 1
#8

Re: Leakage From Transformer Secondary Bushing

12/31/2011 1:36 AM

As is rightly advised the best thing is to take a shut down and rectify the leakage to avoid risk to the transformer.But then the risk does depend upon the extent of the leakage.The essential condition is that the oil level must be all the time visible on the gauge fixed to the conservator tank of the transformer. If the leakage is very small, you may continue to run the transformer by keeping a constant watch on the conservator level gauge.It would not be advisable to run the transformer once the level disappears from the conservator.

Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); gaurav.glory (1); nanronan98 (1); Priyadarshan (1); Ron Nombri (1); Tornado (3)

Previous in Forum: Switchyard Gravel   Next in Forum: Service Factor Less Than 1

Advertisement