Switchyard Gravel

12/27/2011 8:35 AM

substation switchyards surface is often covered with small sized stones (mostly gravel type ).what is the technical reason for it ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#1

Re: Switchyard Gravel

12/27/2011 8:51 AM

C6 crushed stone is cheaper than concrete!

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
2
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Switchyard Gravel

12/27/2011 9:02 AM

To increase the tolerable step potential and tolerable touch potential. Pl. refer to IEEE 80.

Register to Reply Good Answer (Score 2)
3
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3
In reply to #2

Re: Switchyard Gravel

12/27/2011 9:30 AM

In addition, it also helps retarding the evaporation of moisture from the topsoil layer underneath the gravel during dry weather condition. This eventually helps to maintain better grounding resistance (low ground resistance).

Refer to section 7.4 and 12.5 of IEEE 80.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 3)
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#4

Re: Switchyard Gravel

12/29/2011 12:03 PM

To avoid vegetation and growth of grass.

Dhayanandhan.S

Register to Reply
Participant

Join Date: Dec 2011
Posts: 1
#5

Re: Switchyard Gravel

12/30/2011 6:39 AM

Snakes will make shot circuit in the switch yard. As snakes are not able to move on the small stones so gravel(small stones) is provided. This is also one of the reason.

Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

dhayanandhan (1); electricalexpert65 (1); KJK/USA (1); msamad (1); pvcr4 (1)

Previous in Forum: Can We Rotate Tangential Bar Rotor Motor in Both the Direction   Next in Forum: Leakage From Transformer Secondary Bushing

Advertisement