Inverter Duty Motors

05/01/2007 2:06 AM

For inverter duty applications, especially for flame proof applications, do we choose the next higher size or the next frame size of motors for inverter duty applications? Or do motor manufacturers actually manufacture a special motor for that application?What is the actual practice by users?

__________________
Ashok Pillai
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#1

Re: Inverter Duty Motors

05/01/2007 8:31 AM

This day being Labor Day, I am at home without access to my library. What I can remember, however, is that inverter duty motors need to have high insulation ratings.

That said, I've seen standard motors used with inverters without any problems...except for one.

One engineer installed inverter driven motors up at the 6th floor of a building with the inverter sitting inside the MCC at the ground floor. They were wondering why the motors were burning out so quickly. I showed them the voltage at the motor terminals which was over 600VAC from a 440VAC inverter. They relocated the inverters to the 6th floor and haven't had a problem since.

This effect is due to standing waves and would require more explaining than I'd care to do right now. Just keep your cable runs as short as possible. A good inverter manufacturer would put the appropriate cable length in the inverter's manual.

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Associate

Join Date: Apr 2007
Posts: 45
#2

Re: Inverter Duty Motors

05/01/2007 9:16 AM

Thanks, thats great practical stuff. So, unless the inverter is located 'far' away from the drive, the standing wave phenomena that doubles voltage is unlikely to occur?

__________________
Ashok Pillai
Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#4
In reply to #2

Re: Inverter Duty Motors

05/01/2007 9:31 PM

Basically, yes. The thing is you need to determine what frequency your motors are expected to operate at most of the time. If you remember your physics and that thing about string length and frequencies, you'll know what I mean.

A short cable length means that it would take a very high frequency to produce a standing wave which your inverter will probably not be able to generate.

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#3

Re: Inverter Duty Motors

05/01/2007 9:02 PM

The largest difference between inverter duty motors and non-inverter duty motors are...

1) They are designed to run at hotter temperatures as most inverter driven motors run at less then line speed. This reduction in shaft speed slows down the cooling fan and the amount of cooling the motor sees. The temperature rating of the motor's insulation is higher to compensate for the increased heating in the windings.

2) The insulation system is designed to withstand larger pulse voltage that are or can be present on inverter systems.

3) The coil windings are braced better to withstand magnetic wire motion in the winding. Wire motion can cause "abrasion" damage to the insulation system.

All and all it has a lot to do with what you are going to do with the motor/inverter.

For a good document from a reputable manufacturer about non-inverter duty motors on inverters... go see

http://www.usmotors.com/Datasheets/PDF_PDS/pds811-215.pdf

Rick...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#5
In reply to #3

Re: Inverter Duty Motors

05/02/2007 1:11 AM

Adding to the list, they often have insulated bearings to prevent damage due to induced currents.

Almost all manufacturers are building motors for inverter duty. It is well worth the additional cost (if any). If it is not inverter duty and you use it on an inverter and damage occurs, your warranty may be void.

Register to Reply
Associate

Join Date: Apr 2007
Posts: 45
#7
In reply to #5

Re: Inverter Duty Motors

05/02/2007 1:42 AM

You are probably right. The problem is that the motor manufacturers have an extremely long lead time for inverter duty motors (besides a higher price) which suggests that their volumes are not all that large. At the same time there are more inverters sold than ever before. So motor manufacturers either are not responding to the possible volume increases or users are just taking one size higher HP or frame and getting on with their applications. Comments?

__________________
Ashok Pillai
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#10
In reply to #7

Re: Inverter Duty Motors

05/02/2007 12:06 PM

In Canada /USA almost all Reliance motors (now Baldor Dodge Reliance) are stocked inverter duty. I believe Siemens are also. If you have HP & RPM (and range of speed operation), and what country you are in I may be able to give you more precise info.

Register to Reply
Anonymous Poster
#6

Re: Inverter Duty Motors

05/02/2007 1:41 AM

Apart from the factors already raised by others, a suitable dv/dt filter will overcome the standing wave problem [always endeavour to keep both motor and VVVF drive close together]. The motor will obviously require an independantly drive fan, as the shaft driven fan of a TEFC motor is unsatisfactory as low speeds.

Contact me for the dv/dt filter is you need more details.

Greg

Register to Reply
Associate

Join Date: Apr 2007
Posts: 45
#8
In reply to #6

Re: Inverter Duty Motors

05/02/2007 1:47 AM

Thanks, Greg. Is it a LC circuit to filter out the harmonics? Yes, am interested ..

__________________
Ashok Pillai
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#11
In reply to #6

Re: Inverter Duty Motors

05/02/2007 12:22 PM

Another technique is to use a 3 phase output reactor to filter out the high frequency component. This will also allow you to use "standard" motors in most cases, but don't count on warranty support. These reactors are made by people like Hammond, and sold by all the VFD suppliers.

Register to Reply
Active Contributor

Join Date: Oct 2006
Posts: 11
#9

Re: Inverter Duty Motors

05/02/2007 8:04 AM

A few points to mention.

Flame proof application in the Oil & Gas industry (heavy industrial) usually suggests a maxiumum temperature rating for a motor normally refered to as your T-rating. Regardless of wether you are looking for inverter duty or not your T-rating needs to be compared with characteristics of your hazard. One way to lower a T-rating is to increase the size of the motor frame.

Inverter rating is a separate issue, directly addresses the motor insulation rating, inverter duty motors have a higher insulation rating. Inverter rated motors are more rugged in construction because of their severe duty.

A common practice is a power line reactor to clean up the power signal. Normally a standard TEFC motor can be utilized if you take the appropriate steps to limit excessive voltage at the motor terminals. The T-rating of a standard TEFC motor is pretty hard to accurately calculate if you are going to drive it with an inverter.

At this point it is worth pointing out that if you specify an inverter duty motor instead of a power line reactor you need to specify power cable with higher voltage insulation as well. Would be best to install the power line reactor, standard 600V rated cable, and an inverter duty motor. Some will argue for VFD cable regardless.

As you can see the question you are asking is not straight forward. The temperature/ flame proof part of the question could make the engineering more complicated that it seems.

Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#12

Re: Inverter Duty Motors

05/02/2007 12:26 PM

You mention Flame Proof. Do you have the local codes you need to meet? NFP? CSA? NEC? CSA? IEC? City / State codes?

Do you mean explosion proof?

The problem with this forum is it is global and many laws are local.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13

Re: Inverter Duty Motors

05/09/2007 6:51 AM

Other posts are correct in pointing out the higher heat dissipation for a motor running more slowly than normal, partly because of its internal characteristics, and partly because its cooling fan is spinning more slowly. It is important to ensure that the Temperature Class rating of the motor is not compromised as a result.

To make sure, select a certified hazardous area motor-inverter combination, rather than piecing together discrete items of equipment, appropriate for the country of use so as to be on the safe side.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 13 comments