IEE Circuit Design-Over Engineered

01/02/2012 1:58 AM

Dear All first of all I would like to wish you all a HAPPY NEW 2012 YEAR.

What I would like to discuss with you all today is the over-engineered way of designing electrical circuits as per the IEE regulations. Taking a hypothetical example for a normal single phase lighting circuit with 16 Amp MCB and utilizing method 1 installation it would yield a 3 x 4mm2 cable which is somewhat unrealistic. In normal case for lighting circuits we utilize a 1.5 mm2 cable. This is an overkill on design in which no right-minded electrician will utilize in actual designs.

Primarily this over-design solution is the combined effect of the temperature and grouping factors. I believe that the grouping factor is a worst case scenario in which it assumes that all grouped circuits within the same containment are simultaneously working and at full-load, which in reality is rarely the case.

Engineering judgment is vital and one needs to asses what is reasonable and which is not in such installation thus I would like to discuss with you whether do you have the same impression on the issue and other views.

I thank you for your valuable help

Best Regards

Ryan

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: IEE Circuit Design-Over Engineered

01/02/2012 2:24 AM

Always plan for worst case scenario when lives are at risk...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 2)
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: IEE Circuit Design-Over Engineered

01/02/2012 6:00 AM

If one follows the Regulations and certifies it to state that it does follow the regulations, then several things happen:

  • One is protected against claims for damages, negligence and poor workmanship.
  • One remains popular with the end Client's fire insurance company.
  • One's reputation amongst peers remains intact, and one remains in business.

There is something wrong with the calculation that offers 3 x 4mm2 on a 16A MCB. Revisit the calculation and look for procedural and arithmetic errors.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: IEE Circuit Design-Over Engineered

01/03/2012 12:43 PM

Quote Ryan "16 Amp MCB and utilizing method 1 installation it would yield a 3 x 4mm2 cable which is somewhat unrealistic"

1. Why do you need 3x4 mm^2 for lighting. Is that what we call a multiwire ckt, 2 wires sharing a common neutral?

2. 4mm^ is approximately equal to #12 ampacity of 20 amps and is used quite often for receptacles and lighting. Why do you feel it is unrealistic?

3. 1.5 mm^2 is approximately equal to #14 ampacity of 15 amps and is the minimum conductor used for any installation. Often used for ckts to lighting and Rec. What size would you suggest using?

Register to Reply
Associate

Join Date: Jul 2011
Posts: 43
#5
In reply to #3

Re: IEE Circuit Design-Over Engineered

01/04/2012 12:26 AM

Dear wareagle

Thanks for your comment. Well for a 16 Amp load circuit I would normally use the 3 x 1.5 mm2 cable although to be quite honest I would not load the circuit to 16 Amps. One thing that I keep in mind is that the MCB does not "fault protect" at its rated current (in this case 16 Amps) but a (factor) x its rated current for a designated amount of time. here is where you verify IEEs second condition.

Atleast thats what I think...(which is not necessary correct :))

Register to Reply
Associate

Join Date: Jul 2011
Posts: 43
#4

Re: IEE Circuit Design-Over Engineered

01/03/2012 4:33 PM

Apologize for the late reply.

Ok lets say that I have a lightly loaded circuit of about 500 W, single phase thus terminal voltage would be around 230 V (Europe). I(n) MCB rating is 16 Amps and we are going to use for arguments sake method 3 installation. The circuit is along side other 2 circuits.

From the above Load current I (b) is approx 2.18 Amps. From IEE tables

Ca taken to be 1.0 (temp 30 deg. Cel) and Cg to be 0.7 (3 circuits)

from the above therefore I(z) is 16/1/0.7*1.0 is 22 Amps

from table 4D1A fourth column for 22Amps we have 3 x 4mm2.

Not considering the conditions that need to be satisfied we have the following conclusion. a 2.18 Amp circuit is to be wired with a 3 x 4mm2 cable which in my oppinion is too excessive.

When you design you need to make sure that such design is financially practicable and when your out in the industry such considerations matter a lot!!. Its not a question of saftey its a question of good design and judgmnet without jeopardizing saftey.

What do you think?

Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#6
In reply to #4

Re: IEE Circuit Design-Over Engineered

01/04/2012 3:57 AM

I yet to understand your posting. Here in UAE, the maximum lighting circuit allowed upto 1200 W. You could use 16A MCB (Minature Circuit Breaker) and 3X1CX2.5mm2 pvc. Three wires, one for phase, one for neutral and one for earthing. Some people use flex cable but .....In 1200 W circuit, you could have 12 lighting points, even when applying the standard like considering each normal light point of 100 W (regardless the light being of 18W). Chandlier is of 500W and even 1000W.

__________________
--
Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

abasins (1); PWSlack (1); RyanC83 (2); SolarEagle (1); wareagle (1)

Previous in Forum: Automatic Charge/Invert Circuit   Next in Forum: Reverse Power Protection in HT Panel

Advertisement