I need how to operate REF( Restricted Earth Fault ) relay in fault time of transformer ?. And application for REF relay.?
Regesh kumar
Good Answers: 170
Re: REF Relay Operation in Transformer
01/02/2012 7:25 AM
Pl. attend to our training programme on protective relaying.
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member
Location: Chennapattanam (Coromandel Coast of the Bay of Bengal).
01/03/2012 12:13 AM
Restricted earth fault relays are differential relays connected to provide sensitive protection for equipment against ground faults. The most common usage is for the protection of delta-wye transformers with a resistance grounded neutral.
One CT in the transformer neutral is balanced against the neutral of three phase CTs in the transformer output connection (or bushing CTs in the transformer circuit breaker) and connected in parallel. The REF relay is connected across the two CT leads - this relay is a high impedance type, operating on fault voltage developed across the CT leads for an internal fault. For an external earth fault, the zero sequence current in both sets of CTs is balanced and there is no fault voltage developed on the CT leads.
The REF scheme is a high speed differential protection, with instantaneous operation for internal faults and high stability (depending on setting) for external faults.
01/03/2012 3:58 AM
Another duplicate thread? How about entering the words "restricted earth fault relay" into the "Search all of CR4" box on the rhs of the screen?