Correct Valve Selection

01/04/2012 3:22 AM

Dear All,

For a Flare Gas Recovery Unit Application, we have One Valve Termed as Fast Opening Valve with 48." Line size /150# and Opening Time is less than 02 sec, We consider this as Emergency Depressurization with Trip from Compressor Fast Opening Valve should open and Release it to Flare .

We have three options of selecting

High Integrity Ball Valve , ( Line size is 48" , So Lot of weight )

Triple Eccentric Butterfly Valve ( Valve Opening time is 02 sec, so we have concern about the Vibration )

Axial High Integrity Valve ( Problem Vendor cant nmatch delivery schedule )

Please let me know which is the most prefered Valve for this application.

Regards

Jose John

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Correct Valve Selection

01/04/2012 3:44 AM

Only the purchaser can determine the preferred valve, as 'to prefer' involves evaluation of criteria against an internal weighting system.

Surely it has standards for this sort of thing (rhetorical question)?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Correct Valve Selection

01/04/2012 10:08 AM

You'll either have to provide much, much more information or make the decision based on your internal engineering evaluation.

You're there, we're not. Wherever "there" is, which you haven't told us either.

Are you on Saturn?

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Correct Valve Selection

01/04/2012 11:41 AM

I prefer "Triple Eccentric Butterfly Valve", but only because it sounds cool...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jun 2011
Location: Mossel Bay, SA
Posts: 777
Good Answers: 21
#4

Re: Correct Valve Selection

01/05/2012 4:11 AM

My personal choice would be the the butterfly valve, for reasons of weight, size, price and tight shutoff . However, I wonder what your concern is regarding vibration ?

Since your pressure rating is only 150# and this is only a dump valve (not directly connected to vibrating equipment), I don't foresee a problem at all, unless you have not disclosed all relevant information.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2008
Posts: 121
Good Answers: 4
#5
In reply to #4

Re: Correct Valve Selection

01/05/2012 9:02 AM

My choice is buterfly valve. With even less than 90 degree turn, it will give maximum flow .

Register to Reply
Power-User

Join Date: Sep 2011
Location: Near the New Madrid Fault. USA
Posts: 269
Good Answers: 1
#6

Re: Correct Valve Selection

01/05/2012 10:09 AM

I would think a "V-Ball" would be the most failsafe. You need to calculate C/V you have to deal with delta pressure. If you contact your local Fisher-Governor Rep. they will be glad to help you with valve selection, material, actuator etc.

Good Luck

__________________
It's not Rocket Science
Register to Reply
Member

Join Date: Dec 2009
Posts: 8
#7

Re: Correct Valve Selection

01/05/2012 10:12 AM

We have made knife gate valves that were used for this purpose. They have oversized air cylinders with a pressure switch in the lines to trip the valve to open or close. You dont want to get your hand cought in those it would make for a bad day. I have done several of these. The biggest factor is making sure the gate shutting does not destroy the valve, considering the gate is 2-1/4" thick and weighs about 1,500#.

Register to Reply
Associate

Join Date: Jul 2011
Posts: 34
Good Answers: 1
#8

Re: Correct Valve Selection

01/07/2012 3:04 AM

I would choose the ball valve because it presents no impediment to flow when open. My preference is linked to the understanding that in flare knock out drums, use of "internals" is not usually permitted for fear of its clogging/choking the line and resulting in an over-pressure condition. Extending the same philosophy, I lean towards minimizing the "internals" in the flow path.

Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Hilton (1); IRSHAD (1); lyn (1); NEXTMIKEB (1); PWSlack (1); Rockyscience (1); seg (1); SolarEagle (1)

Previous in Forum: Ion Selective Electrodes   Next in Forum: What Is The Difference Between Coplanar And Conventional Transmitters?

Advertisement