What is the difference between making and breaking capacity of mcb, mccb? Also please let me know how to select mcb, mccb with respect to breaking capacity?
As the terms imply, Making Capacity is what the CB can make on to, without damage, and Breaking Capacity is what it can break safely. You should choose a MCB or MCCB whose capacities are higher than the maximum that the system can deliver. For this purpose, you need to be able to calculate the system fault level.
__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Thanks for information. Also, plz let me know how to calculate the fault level in a given system eg control panel. I need to know is there any specific mathematical formula.
The Making capacity is not really higher than the Breaking capacity.
It appears higher because the Making capacity is the PEAK value while the Breaking capacity is expressed as the RMS value. So there is a difference of the sinusoidal peak multiple of √2 as well as the doubling factor due to the DC component. So the making peak current can be as high as 2.2 x the RMS current. Here are the relevent IEC definitions.
It is dangerous, don't you think, to have a higher capacity to make while the breaking capacity is lower?
__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Also refer www.electrical engineering portal.com. Breaking capacity is estimated SC current the PD can break while Making capacity is the highest value the PD can reach under specified(PF)conditions. A circuit can be broken in fraction of a cycle by modern CBs but making current can reach high values depending on circuit parameters like C,L,PF,motor starting,pt in the wave form where it is closed etc. An induction motor takes 6 to 8 times rated current on DOL but its inrush current can reach 20times rated current.
i am unable to reach the two websites that you have mentioned. You know, you can create directly clickable links by using the right click of the mouse after pasting any web address, maybe that will make it easier for others to access the webpages.
Anyway, i can't quite make out...are you disagreeing with the IEC definition of Making and Breaking capacities?
__________________
Nothing worthwhile can ever be taught, it can only be learnt.
I agree with KVS! Making capacity is the maximum value of the "peak" current experienced when the circuit breaker is closing on to a three phase short circuit fault. As explained by KVS, this includes the peak value of the RMS value of the fault current (Root 2 x RMS) and the Aymmetry Factor or the "KHI" Factor, which is due to the DC contribution to the fault from the stored energy in the system reactances (which depends upon the system "X/R" Ratio). This peak value is helpful in claculating the electrodynamic forces (could be attractive force or repulsive force, depeneding upon the contact arrangedment in the breaker) developed during the breaker's closing during a short circuit. Whereas the RMS value of the fault current is useful in calculating the thermal effects of the short circuit current. Peak current does not play a role in breaking capacity, because after a fault, by the time a protective release senses, sends a trip commnad to the breaker and by the time the breaker actually breaks the current, the fault current would definitely have subsided to the symmetrical RMS value from the Asymmetrical peak value (even with the most modern numerical relays and most modern fast acting circuit breakers).
i can't say, since i can't get to those websites as i said before.... please check again whether there is any mistake in typing them. Better still, give the weblinks as i mentioned before, and maybe we can solve the mystery.
__________________
Nothing worthwhile can ever be taught, it can only be learnt.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856