electrical motor have a no name plate so how to determine the motor hp and motor rpm

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: electrical motor

01/14/2012 9:20 AM

If the motor is in place and running, all you need to do is measure the voltage and the amperage which will give you the wattage which will give the hp, around 745 watts per hp....If it's just sitting alone with no history, it's scrap...RPM can be determined with an rpm counter...

http://www.electron.it/pdf/catalogue/LEAFLET%20A47%20SERIES%20(INSTRUMENTS%20FOR%20ELECTRICAL%20MACHINES).pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2

Re: electrical motor

01/14/2012 10:33 AM
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Member

Join Date: Jan 2012
Posts: 6
#3

Re: Electrical Motor

01/14/2012 12:05 PM

Rated HP is difficult to determine.What you do is measure motor RLA and calculate KW.

An RPM meter will measure the speed of motor.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4
In reply to #3

Re: Electrical Motor

01/15/2012 2:26 AM

LRA and No-load Amps, even pf at no load could be measured. Is the LRA at no-load is around 6 times the no-load amps?. It depends on the design code of the motor which is equal to LRA/FLA

__________________
pnaban
Register to Reply Off Topic (Score 4)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5
In reply to #4

Re: Electrical Motor

01/15/2012 12:03 PM

I don't agree that this post is totally Off Topic, just slightly inaccurate for the following reason:

There is no way to easily DETERMINE the mechanical output capability of an unmarked motor, because as mentioned, all you can do is measure RLA, shaft torque etc., but that does not provide you with design limits. But I think that measuring LRA is actually a decent way of ESTIMATING what the designed power rating might be.

However if you don't know what the design VOLTAGE is either, then getting LRA would be problematic in that if the motor was designed for a lower or higher voltage than what you apply to test it, the results would be meaningless.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#6
In reply to #5

Re: Electrical Motor

01/15/2012 11:46 PM

In some countries there is only one LV (400v)for 3ph motors. I was under the impression that the OP is from such a country. In Saudi arabia I have come across 3 standard voltages for LV namely 220,380 and 480. There sump pumps are normally with 220V single phase motors. In our company a pump came for repairs and after rewinding the technician gave 220V and motor burnt. Upon checking we found the rated voltage was 110V. The technician said the name plate was not clear and he was not given a magnifying glass to check the nameplate.If you know how to solve the problem why don't you come out with your solution.

__________________
pnaban
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#7

Re: Electrical Motor

01/16/2012 2:39 AM

Rpm can be measured by a rpm counter.Determining HP is difficult.You have to do atemp ries test either as is done in a factory or if u have some loading device it can be done.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

JRaef (1); msamad (1); nesubra (1); pnaban (2); SolarEagle (1); zaheer khan (1)

Previous in Forum: Borehole Pump Installation   Next in Forum: DC Power Supply

Advertisement