Wiring Meter Utility Box to Distribution Panel

01/18/2012 2:01 AM

Iam in the process of upgrading my home mcb panel and utility meter box.

Location : India

Volts: 240 volts, here we don't have the concept of 120 volts for live/phase wire.

Phase : single phase

MCB ratings:- all the MCBs in the mcb panel are rated as "C16, 6KA" and the double pole MCB in the utility box is rated as "B16, 10000".

Existing wiring scheme : one utility meter box, ground floor mcb panel, one first floor mcb panel. mcb panels feeding to respective ground floor and first floor circuits.

I had googled a lot to understand the method of wiring so that my doubts regarding upgrading process is cleared. but yet i dont get a clear picture to carry on with upgrading process. After few days of search I accidentally got to this website where one of my doubts was already discussed here. "spn mcb and Double pole mcb". I thought of asking my question too here.

Tasks to accomplish

1. I want to enclose the existing open utility meter panel installed on a wooden board into a metal box. the existing setup has a fuse on Neutral wire between Meter and double pole mcb. while upgrading to metal box do i still have to retain the fuse setup as it is.? Is it correct to install a fuse on the neutral wire?

2. I want to upgrade wiring method between my utility meter box and mcb panel. Existing scenario:- As it is a single phase 240v connection from utility meter through DP MCB, the phase/live wire is split to two. i.e one wire caters to ground floor MCB panel and the other wire caters to the first floor MCB panel.

Now I want to remove the split/joint that is taped and want it to be properly directed to Ground floor MCB panel and First Floor MCB panel through a device(may be an mcb). Is it correct to give two phase wires from phase link in meter box as input to double pole mcb so that I have two phase wire as output from that mcb, one going to ground floor mcb panel and the other going to first floor mcb panel?

3. I Want to add power indicator in the mcb panel so that from inside the house i will get to know if there is a power cut from supply company or if the main mcb has tripped or is switched off. Is it correct to draw a phase wire direct from the phase link in the meter box going to the ground floor mcb panel where the power indicator is proposed to be installed.

4. In the meter box do I have to join the neutral from the meter to the earth electrode of my house?

Thank you for your help

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: wiring meter utility box to distribution panel

01/18/2012 4:12 AM

A1: Fuses in neutrals are prohibited under British Standard 7671 on safety grounds. What is the equivalent Indian Standard and what does it say?

A2: No response.

A3: Not if it isn't correctly protected against short circuit. Not if it involves breaking the seal on the supply company's incoming terminals. Is it such an inconvenience to rely on the indication provided by appliances downstream of the distribution board (rhetorical question)? If the indicator were provided and were out, what additional benefit would it convey (rhetorical question)?

A4: It depends on the earthing requirements imposed by the supply company.

Presumably this installation will be inspected and certified correct and safe by a third party before being energised?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#2

Re: Wiring Meter Utility Box to Distribution Panel

01/18/2012 8:37 AM

The utility meter around here once in place belongs to the utility company. To tamper with it to make changes may cause you a fine. Most have seals on them to show if they have been removed. The person that reads the meter will take notice. Even if you have the new electronic type that sends the information down the line they are serialized for identification. Don't know if that is the case in your neck of the woods but I would find out before hand. Once you get them looking the may look deeper into what you have done that may have required a licensed electrician.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Wiring Meter Utility Box to Distribution Panel

01/18/2012 9:18 AM

For your sake and the sake of your family get an electrician to have a look at the set up.

You can not more the utility companies equipment. The use of metal containment for the equipment carries other risks.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Member

Join Date: Jan 2012
Posts: 5
#4
In reply to #3

Re: Wiring Meter Utility Box to Distribution Panel

01/18/2012 10:54 AM

If I had found a quality electrician around my place, I would not have come to google and subsequently to this website at all. this website would remain unknown to me.

for proof please read the following:-

its a new building construction and as per local supply company, home owners are supposed to get the wiring done from the nearest supply company pole to my meter box. The person from supply company who came to install the meter for my home suggested to get the wiring done by an electrician whom he knows very well. I did so, he used 16-4 cable to draw electricity from the supply pole to my meter and he was the one who installed 32A, 240v/415v fuse on the neutral wire coming out from the meter.

I usually do minor repairs at home like replacing damaged switches or sockets, hence iam aware of phase, neutral and earth wires. however I went ahead to google search for professional information about the three wires. Also I had enquired with few other local electricians and everybody said fuse not to be installed on neutral wire. so in order to confirm i posted my question in this website.

Also my intention is not upgrade the wiring for by self instead i wanted to know the correct way of wiring for my situation so that I can discuss with the electrician who woud do the upgrading for me. just to be on safe side

for example had i left the existing wiring at meter board, it would have created problem for me sometime or the other. Only because iam aware of the phase, neutral and earth wires and also with the information available on the internet, i was clear that neutral wire must not be fused. hence, at least for time being, i think that i avoided an electric accident. However I will get it rectified. But my another problem persists-:

I have two MCB panels, one located at ground floor the other located at first floor and being single phase connection i have only one live/phase wire. how to run it to ground floor and first floor MCB panel without splitting it into two wires. one way that i think is possible apart from the way i mentioned in my previous post is to first take the live wire to one of the MCB panel and then loop it to the other MCB panel. but one of the local electrician here said that that way the load on the MCB will become heavy and instead suggested to take two live wires from the single output socket of the main MCB and use one wire for one MCB panel and the other for another MCB panel.

Is it correct? if yes, is there any other clarity method of such installation.

The reason for me to get into all this is because the existing wiring in my MCB panel is cluttered as all the neutral wires are taped and i wish to de-clutter it by installing a neutral link/bar. hence if getting that done , then i thought let me also get the live/phase wire de-cluttered.

Thank you.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: Wiring Meter Utility Box to Distribution Panel

01/18/2012 12:25 PM

Any connection onto the incoming breaker must be sized according to the maximum short-circuit current that the installation can withstand without damage. Once that has been done it matters not whether the connection is split or whether it is looped-in, for the cable size will be the same in both cases.

British Standard 7671 is a good reference, though the installation really ought to be carried out to the latest edition of the Indian equivalent, which is why the question has been asked earlier [see #1 above].

If the electrician carrying out the work has been assessed as competent to the latest Indian standard, then the installation should be right first time; anything else will make the property's owner very unpopular with its fire insurance company.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Jan 2012
Posts: 5
#6
In reply to #5

Re: Wiring Meter Utility Box to Distribution Panel

01/18/2012 8:33 PM

Thank you, so now i will hire the same electrician who did it first and will also ask about the fuse on neutral wire and will update the thread.

Register to Reply
Member

Join Date: Jan 2012
Posts: 7
#7

Re: Wiring Meter Utility Box to Distribution Panel

01/18/2012 11:58 PM

Dear Sir,

Before I reply your question, I want you to hire an electrician from your locality for the job to be completed. You should not attempt to wire your power supply yourself as tempering with meter seal is crime.

1) In the meter box, you should have preferably two pole MCB of at least 40A capacity.

I would suggest you to instal a 40A, RCCB or ELCB with a sensitivity of 30mA. You can retain your fuse setup for additional safety. No fuse is required on neutral wire.

2) Install a MCB box inside your home and split supply in the MCB box by using two MCBs of suitable rating (In your case 16A) for ground & first floor. You can not have both poles of DPN MCB with phase in meter box.

3) You can use Neon indicators for supply indication. However, you can not connect the indicator to meter link. You should connect the same to output of DPN MCB only.

4) Earth wire should not be connected to neutral of supply. It is required for safety of installations & user. Best is to use an ELCB (Earth leakage circuit breaker ) for safety.

I hope the above help with your requirement.

Register to Reply Score 1 for Good Answer
Member

Join Date: Jan 2012
Posts: 5
#8
In reply to #7

Re: Wiring Meter Utility Box to Distribution Panel

01/21/2012 4:14 AM

what should be the breaking capacity of the MCB used in the MCB box to split the phase wire for ground floor and the first floor MCB Box, 6KA/10KA?

the breaking capacity of the other MCBs for circuits in both the MCB box is 6KA as mentioned in my first post. and the breaking capacity of the MAin DP MCB in the Meter Box is 10000 which is think it means 10KA.

Thank you

Register to Reply
Member

Join Date: Jan 2012
Posts: 5
#9

Re: Wiring Meter Utility Box to Distribution Panel

01/22/2012 1:40 PM

I got this para from a pdf on the web.
1)6.2.2 Fuses shall be HRC Cartridge type conforming to I.S.2208 with abreaking capacity corresponding to system fault level. Fuses shall belink type with visible indication. Screw type fuses are not acceptablefor any ratings. Fuses shall be provided only in the phase conductorseven in case of double pole switches, Neutral, wherever provided,shall have suitable links only.
2)2.7.4 On the main switch gear, where the conductors include earthconductor of a 2 wire system or on earthed neutral conductor of amulti wire system or a conductor which is to be connected thereto, thepermanent indication shall be provided to identify the earthed neutralconductor ( Rule 32 (i) of Indian Electricity Rules 1956 refers).


Rule 31 of Indian Electricity Rules 1956:-

Rule 31: Cut-out on consumer's premises:

  1. The supplier shall provide a suitable cut-out in each conductor of every service line other than an earthed or earthed neutral conductor or the earthed external conductor of a concentric cable within a consumer's premises, in an accessible position. Such cut-out shall be contained within an adequately enclosed fireproof receptacle.

    Where more than one consumer is supplied through a common service line, each such consumer shall be provided with an independent cut-out at the point of junction to the common service.
  2. Every electric supply line other than the earthed or earthed neutral conductor of any system or the earthed external conductor of a concentric cable shall be protected by a suitable cut-out by its owner.
Register to Reply
Member

Join Date: Jan 2012
Posts: 7
#10
In reply to #9

Re: Wiring Meter Utility Box to Distribution Panel

01/22/2012 11:44 PM

Dear Sir,

The HRC fuse in the supply was old method. Now, MCB are replacing fuses in domestic power supplies and in the main circuit 10KA rating is fine. 6A MCB is generally used for light and fan circuit of one loop of max. two rooms. Generally one MCB per room light & Fan is preferred. For power circuit of Geyser & AC independent 16A MCB is used. The DP MCB in mains should be of almost 1.5 times of total of all distribution MCBs.

I hope this clears any doubt of placing MCB & DP MCB in mains board. However, for safety, an ELCB or RCCB is preferred in mains supply apart from mains fuse provided by power supply agency.

Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Kuldeep Yadav (2); ozzb (1); PWSlack (2); safaridicor (4); TonyS (1)

Previous in Forum: IEC Cable Current Carrying Capacity Appendix   Next in Forum: Need a Latching Relay at No Power

Advertisement