Need a Latching Relay at No Power

01/18/2012 4:16 AM

We are facing a power dip occasionally in our field.

so we need something to hold the contactor during the dip to keep our motors running.

right now we are experimenting with a coil lock(PQSI coil lock model 1003)

file:///H:/Work/00%20Prabu/7%20TECH%20DOCS/PQSI%20Coil-Locks.htm

kindly let me know is there any other industrial practice used for this situation.

Register to Reply
Pathfinder Tags: holding coil at power dip
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Need a latching relay at no power

01/18/2012 4:25 AM

Er, never mind the contactors, how are the motors to keep running when there is no power to them?

Motor restart without command is prohibited under many nations' electricity regulations!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Jan 2012
Posts: 14
#2
In reply to #1

Re: Need a latching relay at no power

01/18/2012 4:34 AM

u check the details provide by me COMPLETELY.hav a check at the link i have provided.u will understand the facts.

there are situations we need it.

and We need it right now.and we have decided to implement it.

the capacitors do provide that power when there is no power/power dip.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: Need a latching relay at no power

01/18/2012 4:50 AM

"We need it right now.and we have decided to implement it."

Then hire a local engineer who will do your bidding, right now and quit asking strangers to justify a decision you have already made.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #2

Re: Need a latching relay at no power

01/18/2012 4:50 AM

Are these the same 500hp motors as the ones in this thread (the hyperlink won't open from here)?

http://cr4.globalspec.com/thread/75023

If so, then standby generation is needed, not capacitors or latching relays.

Hire an electrical designer locally.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15603
Good Answers: 982
#10
In reply to #4

Re: Need a latching relay at no power

01/18/2012 5:44 PM

They maybe the same motors. We'll probably get the same answers to our questions, too.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Need a latching relay at no power

01/18/2012 6:42 AM

Have you tried Wide Band Contactors and/or Wide Band Coils? Some wide band contactors can pick-up even at 50% of the coil voltage.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6

Re: Need a latching relay at no power

01/18/2012 7:14 AM

Heh heh, do you realise that you have given a hyperlink to a file in your own computer's H drive? How do you expect anyone to be able to access it?

As EE65 says, wide-band coils allow contactors to 'ride through' voltage dips. If the dips are of longer duration, there are mechanical latch units available for contactors from most manufacturers, you can use them.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15603
Good Answers: 982
#8
In reply to #6

Re: Need a latching relay at no power

01/18/2012 10:05 AM

Maybe they'll remove all firewalls to this drive so anyone can read it. Now wouldn't that be a hackers delight.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#7

Re: Need a Latching Relay at No Power

01/18/2012 8:56 AM

What is the nature of the power dip you are talking about? Is there a total voltage loss and for how long? Such implementation must have provision to exclude ANY possibility of restarting if rhe dip time length is more than a pre-determined number of AC cycles AND be foolproof AND comply with local regulations. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#9

Re: Need a Latching Relay at No Power

01/18/2012 4:51 PM

Right, this seems to be a case of momentary voltage sag causing the voltage to drop below the coil holding voltage causing system shutdowns where system ride-thru would be prefered.

kindly let me know is there any other industrial practice used for this situation.

Power quality management springs to mind to ensure smoother grid supply and/or smoother end user supply to the equipment in question. I have never seen an application where this type of problem could not be solved this way cheaper, easier and safer, but again it depends on the particular application (and applicable standards).

The dip would have to be fairly large to cause contactor coils operating of the single or three phase AC voltage to drop below the coil holding voltage. Additionally, if you are using DC control voltage and contactor coils (eg- powered off DC power supplies as part of the control system) then these should already be protected from grid supply voltage drop by a UPS system(s) or similar.

Is this for a whole factory or portable motor application, etc (you do not say)?

__________________
jack of all trades
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#11

Re: Need a Latching Relay at No Power

01/18/2012 7:16 PM

It's not something to be taken lightly. Read this article from my local utility on the subject, it highlights some of the risks involved.

http://www.pge.com/includes/docs/pdfs/mybusiness/customerservice/energystatus/powerquality/voltagesag_ride.pdf

Reconnecting out of sysnch on a motor that slowed down during the sag or loss can create torque transients of up to 15X normal torque and it is well known to cause motor shafts to twist off. You need to be VERY careful with this. It's not for the casual user to undertake.

In that article, they mention one possible solution is to change to using DC coils on your contactors and having a capacitor installed to maintain the coil state. I have seen that used in some applications where the potential losses from shutting down at the wrong moment are well above the potential risks of motor damage. They then go on to mention the technology behind that "coil lock" product you say you are investigating. There are several suppliers out there besides them. I have never used any of them, I don't like the entire concept, but I recognize that sometimes you have to do what you have to do.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#12

Re: Need a Latching Relay at No Power

01/18/2012 11:39 PM

Latch type contactor is suitable for momentary voltage dip not exceeding 500 msec. Otherwise the motor will get slowed down and will take high inrush current when full voltage is restored. This may eventually trip the motor on over current protection. This depends on the size and type of the motor and the load being driven by the motor.

Register to Reply
Commentator

Join Date: Nov 2011
Posts: 56
Good Answers: 1
#13

Re: Need a Latching Relay at No Power

01/19/2012 8:55 AM

I had this problem too, dips how much or for how many cycles long I dont know.I connected a delay off timer across the contactor coils ( set at a very short time) it worked for me and is still working for me. You can use this only for DOL starters but for bigger motors you may have to use what you are currently looking for (coil lock) about which I am also keen about.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#14

Re: Need a Latching Relay at No Power

01/22/2012 8:51 PM

When I clicked the link it says "name changed or unavailable".

__________________
pnaban
Register to Reply
Register to Reply 14 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

debata07 (1); electricalexpert65 (1); jack of all trades (1); JRaef (1); kvsridhar (1); lyn (1); pillay (1); pnaban (1); prabut29 (1); PWSlack (2); redfred (2); SimpleMind (1)

Previous in Forum: Wiring Meter Utility Box to Distribution Panel   Next in Forum: PLCC and OP_GW Communication

Advertisement