VFD & Energy Saving-3: Efficiency of a VFD

01/19/2012 1:19 PM

Dear all,I have a confusion related to the efficiency of a Frequency drive (ABB ACS 800).The manufacturer says that its efficiency is 98 % but the approach I am using to find the efficiency is as

System Description:

6.3 KV comes from the Grid

1. Transformer (Convert 6.3 KV to 690 V and this voltage goes to the input of the VFD)

2. Frequency Drive (Connected to the Induction Motor)

3. Induction Motor 750 KW (Connected to Fan Type Load)

Power Measurements Points:

1. Transformer: Siprotec Realy 7Sj measures power at the input of Transformer. The Display of 7Sj shows many parameters like Power, Voltage, current, Power Factor etc

2. Variable Frequency Drive: The VFD also shows many parameters but here parameter of our interest is Power going out of the VFD to the Induction Motor

Observations:

During normal condition, The power consumed shown by

Transformer (7SJ) = 200 KW (remains in the range 198 to 202 KW)

VFD = 180 KW (Remains between 176 KW to 182 KW)

Efficiency:

It means VFD takes 200 KW and (after passing to the rectifiion, DC bus and Inverter) gives power of 180 KW to the Motor. It means VFD is 90 % efficient and here I am no where near to 98 %.

Something is missing?

What could it be?

Thanks and Kind Regards

Aghvel Niazi

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: VFD & Energy Saving-3: Efficiency of a VFD

01/19/2012 6:20 PM

Two major issues, one less so.

1) you are measuring input power on the transformer primary, thereby adding the transformer losses to your circuit efficiency. Transformer losses can easily be 3-5%. Very valid, but don't blame the VFD for that. If you have a 690V motor, you will have those transformer losses regardless.

2) if the VFD claims 98% eff, you will also see that qualified to mean "at full load", eff drops off as load is reduced. At 200kW from a 750kW motor, you are at less that 30% load. I would not expect more than 95% eff at that load, maybe less.

Less of an issue: measurement error. Non-linear loads such as VFDs are not easy to accurately measure, I doubt the Siprotec relay is capable of any better than +-2% accuracy on normal sine waves, I wouldn't trust them to be any better than +-5% on a non-linear load.

So, your perceived 90%, less 3% losses in the transformer, less another 3% in unrealized eff losses due to decreased load, less another 3% measurement error, I think you are doing pretty well!

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Mar 2010
Location: Islamic Republic of Pakistan
Posts: 124
Good Answers: 14
#2
In reply to #1

Re: VFD & Energy Saving-3: Efficiency of a VFD

01/19/2012 9:29 PM

Thanks for your interest.There is no doubt that your Post is almost a complete answer.

I am going to share some of the other informations

1. We have both type of Loads, CTL and VTL.Most of the Loads operate in the range between 65 -83 % of there rated capacity. Transformers used are Converter Transformers. Efficiency approximately remains in the range between 87 % to 91 %. 91 % is the Maximum one I noticed

2.When we came to the Motors that are below 40 KW and if these motors are operated below the 35 % of there rated capacity, We have even worse cases regarding efficiency even below 80 %

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: VFD & Energy Saving-3: Efficiency of a VFD

01/19/2012 11:14 PM

One major reason why the efficiency appears to drop off so much as load goes down, is because there are fixed losses in the VFD output, what's called "Switching Losses". These are the result of the high speed switching of the transistors that make up the PWM output, the core technology behind what a VFD is. The switching losses are somewhat constant regardless of output speed because it is based on the carrier frequency of the switching. As load decreases with speed, the constant level of switching losses begins to represent more and more of the total load percentage, which ends up as a lower throughput efficiency. So it isn't that the drive wastes more internal energy as the motor slows down, it uses the same amount, but the useful energy is dropping, so the waste looms larger by comparison.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#4

Re: VFD & Energy Saving-3: Efficiency of a VFD

01/20/2012 6:15 AM

@Jef,

Statement 1 : A three phase squirrel cage motor needs both active power as reactive power to run. If supply voltage and frequency remains the same, the reactive power also remains the same, regardless the actual motor load.

Statement 2 : A frequency drive without an active front end, has mostly a simple 6 or 12 pulse passive rectifier at the input.

This means :

  • no power can be send back into the grid,
  • it can only take active power out of the grid
  • power factor of a frequency drive is almost unity

Is it correct to decide out of statement 1 and 2 : A three phase squirrel cage motor takes the reactive power out of the frequency drive and the frequency drive takes this same amount of reactive power as active power out of the supply grid?

This means that when we run a motor with a frequency drive we now have to pay for the reactive power where in the past we took the reactive power (almost free of charge) out of our power factor capacitors.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5
In reply to #4

Re: VFD & Energy Saving-3: Efficiency of a VFD

01/20/2012 10:47 AM

As a tangent to the OPs thread this may have been better suited to be it's own thread, but too late now.

The flaw in your hypothesis is the "reactive power for free" part. In any circuit, you pay for WATTS, which know not from active or reactive. Watts are watts and none of them are free. In a DOL circuit with PFC capacitors, the reactive CURRENT is stored and released by the capacitors, but it all came from the same input watts. So adding caps does not change the watt consumption, but it does releive the supply system from having to supply EXTRA current to facilitate the reactive current. So that is why PFC caps do not save ENERGY (kWh), but they do allow the utility to use more of their available capacity, so they relive you of kVAR demand penalties.

With a VFD, you can think of that reactive current for the motor as being stored and released by the VFD's internal caps, so it essentially performs the same function. This of course is leaving out the entire discussion of displacement vs distortion power factor of course. I was just addressing your question as stated.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#6

Re: VFD & Energy Saving-3: Efficiency of a VFD

01/23/2012 9:57 AM

Dear Mr. Aghvel Niazi,

I tried to reply this yesterday but some internet connectivity problem was there and hence posting to-day.

You know well that any equipment at full Load or near to full load gives best efficiency. But your load is 30% only as stated by you. The VFD Manufacturer will have to give a Performance Graph at various Loads say 25%, 50%, 75% and Full Load and compare the actual performance at your site.

Secondly, pl.do conduct HORMONIC ANALYSIS as it causes some problem and energy is wasted as additional heat which can be controlled.

As indicated by other members, Power Input to be measured at the Input of VFD only and Not even in the Secondary Terminal of the transformer.

Thanks,

DHAYANANDHAN.S

Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Aghvel Niazi (1); dhayanandhan (1); JRaef (3); rudy.leurs (1)