We want to buy copper cable for connecting in coming power and out going to 4 nos of Siemens make VFD units , SINAMICS S150, of 560KW capacity each operating at 415VAC. Can you please suggest suitable cable for the above application.The ambient temperature will be 10 to 45 C (INDIA). Cable will be layed in trenches at a depth of 0.5 to 1.0 meters, which are covered with about 150mm thick slabs. Distance from source to panel about 20 meters.The load is 3 ph 415V, SQCage motors of 520 KW, located at a distance of 50 meters from the panel. The application is for driving mill rolls through a reduction gear box.
We are planning to use 3 runs of 240 sqmm 3.5 core armored copper cable for input side and 3 runs of 3 core(185+95) sqmm shielded VFD copper cable with 3 built in earth wires on out put side of the VFD panel.
Do we have any advantage of using separate single core cables for input side?
Do we have to use shielded cable for input side also or armored is OK?
Please suggest whether our selection of type of cable, no of runs is OK or need some change.
Regards
Engineering Fields - Electrical Engineering - Ron Nombri Engineering Fields - Energy Engineering - Ron Nombri Engineering Fields - Power Engineering - Eternal Power Papua New Guinea - Member - Ron Nombri
Re: Input Out Put Cables for 560kw vfd Panel
01/22/2012 7:40 AM
Please provide the following data on the motor and the VFD:
What is the full load current?
What is the power factor?
What is the efficiency?
Kind regards, Ron
01/31/2012 8:59 AM
Thank you very much for the response. I am sorry I could not respond as I was away. Following is the details:
Motor: 520KW, 415V,50HZ, 994 RPM, 880A
VFD: 560KW, 960A, 415V, 50HZ PF can be adjusted to 1.0
Thanks again.
01/22/2012 8:22 AM
You may use separate single core cables, as long as they are the correct size for the input. In most cases 3 core shielded cables are used.
From experience I have installed shielded cables for power supply and controls. Shielded cables are required where the cables are run near/along side other power cables, where magnetic effect from other cables may affect the supply on the controls cables/power cables.
Please provide data on full load current, power factor, and efficiency of motor and VFD. Knowing your motor full load current, you may select the right cable which can be installed at a depth of 0.5 to 1 meter and still be able to supply the required full load current of the motor, at the required efficiency and power factor. Look up cable selection books and importantly the VFD manual for installation guides.
Kind regards, Ron
Good Answers: 181
Re: Input Output Cables for 560kW VFD Panel
01/22/2012 8:22 PM
Instead of trusting complete strangers on the internet, why not employ a local engineer that knows your local codes.
01/23/2012 1:39 AM
Srinivasan,
The cable selection seems fine given our Indian power conditions. Although you can use a three core cable, the cable size would be quite large in cross section. A single core 630 sq. mm copper cable should be able to give you 1254 amps current under open air / conductors in conact with each other and at 70 deg conductor temperature and an ambient of 30 deg. C for type N2XH power cables. Ambient rising to 45 deg. should not pose a problem with 3 runs of 240 sq. mm per phase. Source: HELUKABEL gmbH
Do not overlook a filter on the input & output side for suppression of harmonics. Shielded cable gives you further protection in terms of EMI / EMC. Surge protection devices if planned would also benefit you in the long run.
In case of any further queries, I am on
CR4 Admin - phone number removed
From the CR4 Rules: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers and email addresses posted in threads or comments. You can share this information via the CR4 internal messaging system.
01/23/2012 3:34 AM
Use the Indian equivalent of British Standard 7671.