Sir,
We want to buy copper cable for connecting in coming power and out going to 4 nos of Siemens make VFD units , SINAMICS S150, of 560KW capacity each operating at 415VAC. Can you please suggest suitable cable for the above application.The ambient temperature will be 10 to 45 C (INDIA). Cable will be layed in trenches at a depth of 0.5 to 1.0 meters, which are covered with about 150mm thick slabs. Distance from source to panel about 20 meters.The load is 3 ph 415V, SQCage motors of 520 KW, located at a distance of 50 meters from the panel. The application is for driving mill rolls through a reduction gear box.
We are planning to use 3 runs of 240 sqmm 3.5 core armored copper cable for input side and 3 runs of 3 core(185+95) sqmm shielded VFD copper cable with 3 built in earth wires on out put side of the VFD panel.
Do we have any advantage of using separate single core cables for input side?
Do we have to use shielded cable for input side also or armored is OK?
Please suggest whether our selection of type of cable, no of runs is OK or need some change.
Regards