psl some one help me....

Why capacitor bank should be turned off while starting the disel generators DG.....????

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: why capacitor shld be OFF while starting generator

01/23/2012 5:41 AM

Er, to prevent the circuit protection devices upstream of them operating, perhaps?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Why Capacitor Should Be Off While Starting Generator

01/23/2012 9:04 AM

To avoid hunting of generator AVR

To avoid failure of Surge Suppressor in the Rotating Rectifier

To avoid failure of generator winding insulation

Register to Reply Good Answer (Score 2)
Associate
India - Member - New Member

Join Date: Oct 2009
Location: INDIA
Posts: 49
Good Answers: 1
#3

Re: Why Capacitor Should Be Off While Starting Generator

01/27/2012 5:27 AM

During starting of gen set usually it is in no load, if the capacitors are connected stator MMF aid the rotor MMF are additive which leads to increase in voltage, now when the gen set is loaded Voltage drops drastically. In this condition AVR cant compensate the voltage drop with in the safe time limit.

__________________
key questions why, what & how - just think
Register to Reply
Active Contributor

Join Date: Jan 2012
Posts: 14
#4

Re: Why Capacitor Should Be Off While Starting Generator

03/04/2012 9:26 AM

Capacitors should be kept in OFF condition because it acts as a load for Diesel gensets.Thats why DG sets are rated in KVA.While coming to Power plant alternators capacitors are switched ON to maintain P.F.

Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); parvathaneni (1); PWSlack (1); sathish-47 (1)

Previous in Forum: Insulation Resistance Test   Next in Forum: Voltage in Saudi Arabia

Advertisement