High Neutral Current

01/25/2012 10:02 PM

Dear all,

We have 2 same sets 400 VLL/50Hz/1000 kVA, both are same model and brand,for generator made by stamford and sets operation in parallel, let say G#1 and #2. 2 months ago G#1 generator damaged, phase V on main stator winding got burn. After repaired done, we test G#1 for single run - ok, balance voltage and amperage of load. When G#1 parallel with #2 , voltage/frequency/drop were adjusted same but the neutral amperage on G#1 was 700 amps when at G#1 U=912A V=936A W=915A. So, we sent back to get check again for winding. After second return, problem still persist.

What could be cause of this ? because when we tried with our generator spare that has same frame/model/capacity there is no high current on neutral.

Please advise...

Very much thank you

__________________
One system
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: High Neutral Current

01/26/2012 5:24 AM

One of the possibilities is a shorted turn on G#1's windings, causing one of the phases' voltages to dip relative to neutral. What are these voltages?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jan 2011
Location: Jakarta
Posts: 162
#2

Re: High Neutral Current

01/26/2012 5:42 AM

Hi PWSlack,

From 400 VLL at 0A voltage drop to 398 VLL, these are same voltage drop on G#2. We already test for single load 100% kW and neutral current only 10A. What is shorten turn on winding ?.

__________________
One system
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: High Neutral Current

01/26/2012 5:49 AM

Another possibility is that the load on one or two of the three phases is almost all capacitance on G#1.

It's a bit difficult to see from here, though.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jan 2011
Location: Jakarta
Posts: 162
#4

Re: High Neutral Current

01/26/2012 8:26 PM

Hi PWS,

But when I used with other generator and couple with sane engine, using the same component and power line - neutral current not more than 15A.

__________________
One system
Register to Reply
Associate
India - Member - New Member

Join Date: Oct 2009
Location: INDIA
Posts: 49
Good Answers: 1
#5

Re: High Neutral Current

01/27/2012 12:19 AM

as you have said that alternator has re winded, has the winding is done for damaged phase or complete winding has changed chances for this problem are

unequal turns for 3 phases

improper neutral grounding

change in winding sequance

__________________
key questions why, what & how - just think
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#6

Re: High Neutral Current

01/27/2012 3:59 AM

Use a power analyzer or oscillioscope and check the waveform of voltage,current, frequency in phases and neutral whether there are harmonics.

__________________
pnaban
Register to Reply
Participant

Join Date: May 2007
Posts: 2
#7

Re: High Neutral Current

02/02/2012 3:21 PM

I think the generator # 2 is wrong rewind so the sum of currents the two generators operating in parallel is out of normal phases genrating high neutral currents.

For exmple, with measured current values, suppose the current "A" (912 Amps) at zero degrees, the current "B" (936 Amps) with a -145 degrees and current "C" (915 Amps) wit a -205 degrees lag, result in a neutral current of 700 Amps.

Is recommended the measurement of the angles of phase of line voltages on the generator # 2.

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jan 2011
Location: Jakarta
Posts: 162
#8

Re: High Neutral Current

02/02/2012 7:41 PM

Dear Gentlemen,

Thanks for your great explanation. This G#2 generator rewind by local workshop and conclution is not far from rewinding the generator, and best thing is to repair it to stamford dealer.

Thank you

__________________
One system
Register to Reply
Commentator
Engineering Fields - Power Engineering - Siswanto

Join Date: Mar 2008
Location: JAKARTA. INDONESIA
Posts: 73
Good Answers: 15
#9

Re: High Neutral Current

02/04/2012 1:43 PM

To Pak Yudha

Sorry I just flight back from Poso to inspection, Testing and Supervising the Hydro Power Plant 3x65 MW, New Construction.

Your G#1 when solo running is ok . its look Good, Balance voltage and current during in Load operation, but when synchronize your G#1 get high current.

Your G#1 Generator seem loaded high current circulation from the system due to wrong installation of static CT on this Generator.

Please check the connection for the static CT , its should be on the "V" phase, and should be same stator lead outgoing cables with refer to G#2.

I understand that your G#1 was rewound, but the rewound servicer was wrong connection of the CT. may be they have missing data where is should installed this CT

As you know that the stator out going may have 6 or 9 or 12 outgoing cables, Static CT should be installed at phase "V" and should have same lead with the G#2

Reversing or wrong connection this CT can create high circulating current from G#2 to G#1, that why your G#1 was loaded at the Neutral point, this phenomena's is similar with the reverse power.

Secondary CT connected to AVR with polarity code 'K - L", please do not reverse this terminal, and when generator connected in parallel with the other Generator, make sure that the K-L termination at the AVR is open not to be shorted.

Your G#1 Stator winding is OK !!, the problems is wrong current distribution during in synchronize due to reversing of CT polarity or wrong installation on the Stator Outgoing Lead

The static CT is use to control load power sharing during in synchronize

Following is figure may can help you as reference

__________________
LOVE FORUM AND DISCUSSION
Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jan 2011
Location: Jakarta
Posts: 162
#10
In reply to #9

Re: High Neutral Current

02/05/2012 7:54 PM

Hi Pak Siswanto,

Thank you for your input, We missed to check that & we'll check it again.

Regards,

LS

__________________
One system
Register to Reply
Anonymous Poster #1
#11
In reply to #9

Re: High Neutral Current

04/20/2014 3:12 PM

Sir , Thanks about this point,

But I want to know why is the location of CCCT affect the neutral current??

THX

Register to Reply
Register to Reply 11 comments

"Almost" Good Answers: