Neutral Displacement Relay Fault

02/03/2012 6:42 AM

I was running machine (15MW generator Hydro Power Plant) during starting machine fails to rotate before synchronization, when i check alarm... it says at generator side neutral displacement fault....is it connected to Earthling system of generator...or may someone suggest me what to do????

Rgds

Sunday

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: NEUTRAL DISPLACEMENT RELAY FAULT

02/03/2012 6:52 AM

Isn't it time the original equipment manufacturer's local technical representative was called in to help?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Jan 2010
Posts: 12
#2

Re: Neutral Displacement Relay Fault

02/13/2012 6:06 PM

I believe neutral displacement relay will show as 59BN on your protection single line. If I was listening, when it was explained to me, it protects your neutral free bus, between your generator breaker ( synchronising breaker ) & your generator transformer, from earth faults, prior to synchronism, after which you have a neutral, at the generator, & neutral associated protection to take over for earth fault protection. The relay does some clever Maths, to calculate a theoretical rise of neutral potential, due to fault. The VT used may show an open delta connection arrangement. The delta is open at one corner. I would start by checking VTs, or VT secondary fuses / mcbs, though your relays may already cover this as a separate VT fuse fail function. Hope this helps, Colintonybone

Register to Reply